I have a CM9000 (firmware 7.201) with a LEM01-M2.
Initially there were three SEMs attached (all firmware 7.207) with the first and second SEMs being the older SEM01-M2 boards and the last one being a new SEM01C (but with the old SEM01-M2 power supply board). The first one has a LEM01-M2 but not yet the 2nd or third. Each of the four locations has it\'s own AC power supply and battery all have 0VDC commoned.
The problem with the above configuration was zone troubles on the zones of the 2nd SEM01-M2 - jumpers are set for no EOL resistors. I\'ve removed the cables and have directly connected switches for testing but the problem persists. The zone announcements appear to be working correctly but the zone trouble is also announced. I have not yet configured the last SEM (other than setting the ID to 3). If I bypass these zones, the zones are no longer announced, but the trouble announcements still occur.
I then replaced the first SEM01-M2 with a new SEM01C (but also with an old SEM01-M2 power supply board) and set it\'s ID to 2. The problem persists. Further, on this new SEM01C, the \"Use Shunts\" setting is the default and cannot be changed. The last SEM (also SEM01C) correctly shows \"No EOL\".
All SEMs are being polled but the 2nd & 3rd ones are reporting the Serial Number as \"Invalid\" while the first one reports \"Unassigned\". And the trouble zones appear to be correctly showing Active or Inactive.
This has me rather stumped and I\'d appreciate any advice.
Initially there were three SEMs attached (all firmware 7.207) with the first and second SEMs being the older SEM01-M2 boards and the last one being a new SEM01C (but with the old SEM01-M2 power supply board). The first one has a LEM01-M2 but not yet the 2nd or third. Each of the four locations has it\'s own AC power supply and battery all have 0VDC commoned.
The problem with the above configuration was zone troubles on the zones of the 2nd SEM01-M2 - jumpers are set for no EOL resistors. I\'ve removed the cables and have directly connected switches for testing but the problem persists. The zone announcements appear to be working correctly but the zone trouble is also announced. I have not yet configured the last SEM (other than setting the ID to 3). If I bypass these zones, the zones are no longer announced, but the trouble announcements still occur.
I then replaced the first SEM01-M2 with a new SEM01C (but also with an old SEM01-M2 power supply board) and set it\'s ID to 2. The problem persists. Further, on this new SEM01C, the \"Use Shunts\" setting is the default and cannot be changed. The last SEM (also SEM01C) correctly shows \"No EOL\".
All SEMs are being polled but the 2nd & 3rd ones are reporting the Serial Number as \"Invalid\" while the first one reports \"Unassigned\". And the trouble zones appear to be correctly showing Active or Inactive.
This has me rather stumped and I\'d appreciate any advice.