#21
take a photo of the Comfort to DM02 connectiion and the DM02 with connections
If the photos are too large for attachments, send to support@cytech.biz

This may help to identify any problems
Reply

#22
Hi
RS485 terminal on comfort is occupied by four way cable connection with UCM JP2 , AND the DM02 is connected to comfort by ka/kb and 12v /GND -12V/COM (I assumed this connection is alternative to 4 way cable connection )

Kindly advice.

Please note that prior to connecting UCM, DM02 was connected using 4 way cable to comfort and then also it was the same situation (no telephone bell, no SW2 test cell and no lights on at DM02,however before and now both times the light at DS02 is on)
Reply

#23
Hi, kindly find attached pic showing connections between comfort and UCM and DM02.

Thanks and regards
Alex


Attached Files Thumbnail(s)
   
Reply

#24
I would remove the cables you have connected ka/kb and 12v /GND on the DM02.
Use one of the 4way RS485 cables and connect that between the UCM and the DM02 so that they are daisy chained from the Controller board to the UCM and from the UCM to the DM02.
Make sure that the UCM and the DM02 are set to an ID of 1.
Load comfigurator and from the modules tab right click on Controller and do a \"Scan for all modules\" then check the UCM section a General UCM should be listed check the DoorStations section and the DM02 should be listed.
If both devices are now listed then right click on Controller and do a \"Write modules and settings to Comfort\" the comfort should then reset.
Reply

#25
What is the Number of Door stations in Modules and Settings
If it is 0 then Comfort does not poll the DM02

Reply

#26
I did connect DM02 to UCM and UCM to Comfort as suggested by bs85, however there Is no change . Comfigurator still does not find door station when I scan for it .
Reply

#27
Hi, door station issue resolved
I manually added door station in comfigurator and then wrote the configuration to comfort . Now the bell is ringing on telephone
Reply

#28
In Modules, right click Door station and select Add Door station to add manually
Then write to comfort
Reply

#29
Yes the DM02 has a minimum version before it can be detected by scanning.
Reply

#30
Hi are there any other limitations of this DM02 being older version ? Apart from not being able to appear in scanning
Reply