Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi
I want to use one of the standard alarm inputs to check the status of a device 00/01
The input type must be similar to a RIO input. What should the zone type be for alarm input to report the status of an input without triggering an alarm situation ?
Thanks
Posts: 1,200
Threads: 262
Joined: Mar 2007
Reputation:
0
Zone Type Digital N/O (Normally Open)
will not activate an alarm, and allows you to set the Zone shunt in the Double EOL position (Away from the terminal block) without using EOL resistors
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi,
Please explain what is meant by \'allows you to set the Zone shunt in the Double EOL position (Away from the terminal block) without using EOL resistors\'
or refer me to the manual for more details.
Thanks
Posts: 1,200
Threads: 262
Joined: Mar 2007
Reputation:
0
Normally when the zone shunts are set in \"Double EOL\" Position , ie away from the terminalk blocks you need to use two EOL resistors 4.7K in parallel and 2.7K in series with the sensor contact, otherwise the system will report Zone Trouble
With the Digital N/O or N/C zone types you do not need EOL resistors
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi
Please excuse my ignorance.
I am using Zone 15 to check is the device is on or off. The zone is shunted and no resistors are used.
This is not reporting the correct input zone status, always reports 00.
Do I need to remove the shunt ?
Thanks
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi
I set Zone 15 to Zone Type 30 or 31 (which ever is digital N/O, can\'t remember)
I am using Configurator V223.
I am using the board stock stand, no EOL
Thanks
Posts: 1,200
Threads: 262
Joined: Mar 2007
Reputation:
0
Have you set the zone shunt to Double EOL ie away from the terminal Block?
Remove the terminal block
Go to Keypad F3,2 for Security check
Use a wire to short and open the zone
This should cause the zone to be announced
If it does then the zone setting is correct and whatever is connected to your zone is causing the problem
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi
How do I do this ? ie
set the zone shunt to Double EOL ie away from the terminal Block
Thanks
Posts: 1,200
Threads: 262
Joined: Mar 2007
Reputation:
0
Yes, as I mentioned in my earlier post and in the manual
Away from the terminal block