Version 8.001
Bugs - BUG from 17/4/24 7.230 alarm type dial index always announce 0,0,0,0 on keypad
- For Ultra - EEPROM locations are incorrect for Time programs, sunset response sunrise response, doorphone response, HVAC
- Transfer > Upgrade Sentences fails at LCD keypad words (No Bug for Arm Version)
- From firmware 7.198 - If UCM/knx, UCM/CBus, UCM/Modbus has address mapped to Flag, Comfort broadcasts the flag to all UCMs but the source ID of the UCM changing the flag is not sent correctly by Comfort. This may cause the UCM to send an extra unneccesary message back to the external Interface for KNX, CBus, Modbus etc. This does not cause the UCM not to work , it just causes an extra message to be sent back to the Interface
- Battery check F3,1 when battery disconnected is delayed by 10 seconds and some times does not work from 7.22
- Battery disconnected does not work when there is no battery
- u?82 and higher causes system reset for ULTRA
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes and Bug Fixes- fixed BUG OPTIMUM Only - F2 home control cause wrong announcement
- Fixed bug from V7.255 engineer menu 6789 7,43, announce firmware announce was blank
- Fixed bug ULTRA CMS Format was at wrong address so cms could not dial out
Last edited on Wednesday Apr 9th, 2025 05:19 am by slychiu
|
Posted: Monday Oct 21st, 2024 10:06 am |
|
2nd Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.003
Bugs - Action 200 open door Response caused reset
- zone announce on zone off says Zone Trouble
- BUG from 7.230 alarm type dial index always announce 0,0,0,0, on keypad
- Sunset Response pointed to the wrong EEPROM location. m,ay cause unexpected results due to the contents of the eeprom location
- Transfer > Upgrade Sentences fails at LCD keypad words (No Bug for Arm Version)
- if virtual input is activated, the 1st non-virtual zone activated will cause momentary zone trouble
- From firmware 7.198 - If UCM/knx, UCM/CBus, UCM/Modbus has address mapped to Flag, Comfort broadcasts the flag to all UCMs but the source ID of the UCM changing the flag is not sent correctly by Comfort. This may cause the UCM to send an extra unneccessary message back to the external Interface for KNX, CBus, Modbus etc. This does not cause the UCM not to work , it just causes an extra message to be sent back to the Interface
- Battery check F3,1 when battery disconnected is delayed by 10 seconds and some times does not work from 7.22
- Battery disconnected does not work when there is no battery
- u?82 and higher causes system reset for ULTRA
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes and Bug Fixes
Fixed bug for incorrect for Time programs, sunrise response, doorphone response, HVAC- BUT Sunset response was not fixedLast edited on Wednesday Apr 9th, 2025 05:19 am by slychiu
|
Posted: Monday Oct 21st, 2024 10:06 am |
|
3rd Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.010
Bugs- Sunset Response pointed to the wrong EEPROM location
- Transfer > Upgrade Sentences fails at LCD keypad words (No Bug for Arm Version)
- From firmware 7.198 - If UCM/knx, UCM/CBus, UCM/Modbus has address mapped to Flag, Comfort broadcasts the flag to all UCMs but the source ID of the UCM changing the flag is not sent correctly by Comfort. This may cause the UCM to send an extra unneccessary message back to the external Interface for KNX, CBus, Modbus etc. This does not cause the UCM not to work , it just causes an extra message to be sent back to the Interface
- Battery check F3,1 when battery disconnected is delayed by 10 seconds and some times does not work from 7.22
- Battery disconnected does not work when there is no battery
- u?82 and higher causes system reset for ULTRA
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes and New Features- fix bug if virtual input, If another input active still has virtual input_flag set, zone trouble may occur when new zone activated while virtual input is active This bug existed from the time Virtual Inputs was introduced and the combination rarely occurs
- Fixed other bugs in version 8
- Dial to CMS - If no kissoff is received, only 1 attempt without redial instead of 3 attempts. However Comfort will redial the CMS after each dial cycle. This change reduces the time taken to dial to CMS if a kissoff is not received - as immediate redial always fails
Last edited on Wednesday Apr 9th, 2025 05:19 am by slychiu
|
Posted: Monday Oct 21st, 2024 10:06 am |
|
4th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Bugs- From firmware 7.198 - If UCM/knx, UCM/CBus, UCM/Modbus has address mapped to Flag, Comfort broadcasts the flag to all UCMs but the source ID of the UCM changing the flag is not sent correctly by Comfort. This may cause the UCM to send an extra unneccessary message back to the external Interface for KNX, CBus, Modbus etc. This does not cause the UCM not to work , it just causes an extra message to be sent back to the Interface
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Version 8.011- Fixed Bug Sunset Time Response did not work
- If file system in comfort is wrong eg Ultra should have File System 34 but for some reason the wrong file system was loaded, then the plug in ETH03 on CM9001 could not log in. This has been fixed in 8.011
- Battery check F3,1 when battery disconnected is delayed by 10 seconds and some times does not work from 7.22
- Battery disconnected does not work when there is no battery
- u?82 and higher causes system reset for ULTRA
Last edited on Wednesday Apr 9th, 2025 05:20 am by slychiu
|
Posted: Tuesday Oct 22nd, 2024 05:46 am |
|
5th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Bugs- From firmware 7.198 - If UCM/knx, UCM/CBus, UCM/Modbus has address mapped to Flag, Comfort broadcasts the flag to all UCMs but the source ID of the UCM changing the flag is not sent correctly by Comfort. This may cause the UCM to send an extra unneccessary message back to the external Interface for KNX, CBus, Modbus etc. This does not cause the UCM not to work , it just causes an extra message to be sent back to the Interface
- Battery check F3,1 when battery disconnected is delayed by 10 seconds and some times does not work from 7.22
- Battery disconnected does not work when there is no battery
- u?82 and higher causes system reset for ULTRA
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Version 8.013- Fixed BUG (Not applicable to ARM)- Upgrade Sentences/ Keypad failed at Keypad LCD words stage, Keypad shows Incompatible (applies to non-ARM firmware only - ARM firmware does not have this bug)
- 32 Counters and all 256 Flags are saved in EEPROM at reset (applies to ULTRA only. EMS, LGX, UCM/LOGIC and KNX/Logic already has this feature. Optimum has not implemented this feature). WARNING! if you upgrade to this firmware or later from an older version. initially all flags and 32 counters will be set to on (or 255 for counters)/ If you have flags or counters programmed to actvate some function disable these fnctions when you u[grade the firmware
Last edited on Wednesday Apr 9th, 2025 05:20 am by slychiu
|
Posted: Wednesday Nov 20th, 2024 12:47 am |
|
6th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.015
Bugs- Battery check F3,1 when battery disconnected is delayed by 10 seconds and some times does not work from 7.22
- Battery disconnected does not work when there is no battery
- u?82 and higher causes system reset for ULTRA
- IRIO01 lost comms does not report, restore does not report
- SN01 from eth0 plug in gave wrong value, but from ucm is correct
- b?00 bypass request bits from ETH03 plug in s correct but from ucm is wrong
- Home control menu announces press # to end only for ARM firmware
- GSM dial to CMS sometimes times out waiting for kissoff from CMS
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
New Feaures- For Ultra Firmware the 1st 32 Counters 0 to 31 and All 256 flags are saved in EEPROM,so the values are retained after reset or power off. This is already done in KNX/Logic, EMS, UCM/Logic, LGX01, But Not for Optimum firmware. WARNING! if you upgrade to ULTRA firmware 8.013 or later from an older version before 8.013 . initially all flags and 32 counters will be set to on (or 255 for counters). If you have flags or counters programmed to activate some function disable these functions when you upgrade the firmware.
- Fixed Bug From firmware 7.198 - If UCM/knx, UCM/CBus, UCM/Modbus has address mapped to Flag, Comfort broadcasts the flag to all UCMs but the source ID of the UCM changing the flag is not sent correctly by Comfort. This may cause the UCM to send an extra unneccessary message back to the external Interface for KNX, CBus, Modbus etc. This does not cause the UCM not to work , it just causes an extra message to be sent back to the Interface
Last edited on Wednesday Apr 9th, 2025 05:20 am by slychiu
|
Posted: Monday Jan 20th, 2025 01:04 am |
|
7th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
WARNING! if you upgrade to ULTRA firmware 8.013 or later from an older version before 8.013 . initially all flags and 32 counters will be set to on (or 255 for counters). If you have flags or counters programmed to activate some function disable these functions when you upgrade the firmware.
|
Posted: Monday Mar 17th, 2025 03:06 am |
|
8th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.018
Bugs- SN01 from eth0 plug in gave wrong value, but from ucm is correct
- b?00 bypass request bits from ETH03 plug in s correct but from ucm is wrong
- In test mode failed AC power off detection bug from 19/1/25
- virtual input on zones 1 to 16 did not work
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is announced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes- Fixed BUG from 20/1/25 IRIO comms trouble did not detect
Version 8.020 Bugs- SN01 from eth0 plug in gave wrong value, but from ucm is correct
- b?00 bypass request bits from ETH03 plug in s correct but from ucm is wrong
- In test mode failed AC power off detection bug from 19/1/25
- virtual input on zones 1 to 16 did not work bug
- For ARM only, virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes- y?00 request_fixed BUG caused reset
- TExx test eeprom enhanced command xx = 01 for 1st eeprom, 02 for 2nd eeprom if no xx then xx=1 eg TE01, TE02,.
- Fixed some bugs in KNX/Logic
- Improved Battery disconnect test for ARM. When battery is not connected, F31 detects low bat consistently and immediately now. Before it sometimes did not detect low battery and was always delayed by 10 seconds.
- u?84 and SN84 causes firmware to reset due to overwrite of caused IRIO not to have rs485 comms trouble when disconnected
- When DC input is switched off during Battery test D? does not show very low DCVOLTAGE
- Prevent Battery disconnnect test during firmware upgrade
- If battery is low or disconnected Firmware upgrade will cause UBF7 error
Last edited on Sunday Apr 13th, 2025 03:51 am by slychiu
|
Posted: Monday Mar 17th, 2025 03:09 am |
|
9th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.021
Bugs- SN01 from eth0 plug in gave wrong value, but from ucm is correct
- b?00 bypass request bits from ETH03 plug in is correct but from ucm is wrong
- Home control menu announces press # to end only for ARM firmware
- GSM dial to CMS sometimes times out waiting for kissoff from CMS
- In test mode failed AC power off detection bug from 19/1/25
- zones higher than virtual input dont work they are seen as virtual
- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes- Fixed BUG for ARM only. virtual inputs do not work correctly. When they are activated, they will reset to the state of the physical input
- Battery disconnect test improved for Slave
Last edited on Wednesday Apr 9th, 2025 05:26 am by slychiu
|
Posted: Monday Mar 17th, 2025 03:15 am |
|
10th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.023
Bugs- ARM In test mode failed AC power off detection bug from 19/1/25
- zones higher than virtual input dont work they are seen as virtual
- Enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes- Delete Mailboxes deletes engineer code as well as all user codes. The problem is many installers who installed systems for end users cannot be found anymore. If they changed the default engineer Code, then users or new installers cannot log in.
- ETH03 on CM9001 log on can read serial number correctly. [size="2" style="font-size: 10pt"]Fixed BUG SN01 returns wrong value when connect by eth03 plug in
- Fixed Bug b?00 using ucm replied b?00FFFFFFFFF
- Dial out to CMS increased time out to wait for kissoff from 2 to 4 seconds to reduce chances that kissoff is not received in time
- Fixed bug home control menu did not work , was always empty "press # for previous menu"
Last edited on Wednesday Apr 9th, 2025 05:24 am by slychiu
|
Posted: Saturday Mar 29th, 2025 07:42 am |
|
11th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.024
Bugs- "enter new code and # key" is anounced for change/add user code on keypad after entering new code 2 times, but new code is actually accepted. bug for Toshiba only not ARM
Changes- Fixed bug- test mode failed ACOFF (affected production test only, no difference for actual usage)
Last edited on Wednesday Apr 9th, 2025 05:22 am by slychiu
|
Posted: Sunday Apr 13th, 2025 03:56 am |
|
12th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5846 |
Status: |
Online
|
back to top
|
Version 8.027- Fixed BUG any zone number higher than a virtual input will also effecitvely be virtual
- Fixed BUG for Toshiba only from 5/12/23 "enter new code and # key" is announced for change/add user code on keypad after entering new code 2 times,
|
|