Found out today that worryingly none of the smoke detectors in my house work. I'm guessing the electrician who originally wired them did not get it right.
style="background-color: rgb(255, 255, 255);"These are the detectors: style="background-color: rgb(255, 255, 255);"https://www.apollo-fire.co.uk/getattachment/Products/Range/Series-65/Mounting-Bases/45681-201APO-Series-65-Diode-Base/20001999_0001.pdf style="background-color: rgb(255, 255, 255);"
style="background-color: rgb(255, 255, 255);"The alarm side wiring seems to be green and white connected to the zone input (One per detector) and red and black connected to 12V power, shunts set to 1-2 and Comfigurator Fire NC. I attach a picture of the detector side wiring; cant see any resistors anywhere. Can anyone see what might be wrong?Attachment: SDWiring.jpg (Downloaded 52 times)
|
Posted: Sunday Dec 16th, 2018 02:00 am |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5670 |
Status: |
Offline
|
back to top
|
Sorry cant see amy of yhe file attachments
|
Posted: Sunday Dec 16th, 2018 09:20 am |
|
3rd Post |
Swiss-Toni
UCM Pi Users
back to top
|
Is that a red wire going into the negative & where is the positive wire! looking at it does not look like this has been wired up with any power - + based on the colour of the cables that you have used and without a wiring diagram!
Last edited on Sunday Dec 16th, 2018 09:23 am by Swiss-Toni
|
Posted: Sunday Dec 16th, 2018 05:11 pm |
|
4th Post |
Krobar
Member
Joined: | Saturday Oct 19th, 2013 |
Location: | |
Posts: | 27 |
Status: |
Offline
|
back to top
|
Swiss-Toni wrote: Is that a red wire going into the negative & where is the positive wire! looking at it does not look like this has been wired up with any power - + based on the colour of the cables that you have used and without a wiring diagram!
Thanks for the reply.
The red goes into "-" on the PCB, the black wires goes into "L1In", these 2 are connected to 12V power on the Comfort. The White and green wires go into "NC" and "C" on the PCB and these are connected to the zone input on the Comfort. I tested 3 of the detectors with canned smoke and none reacted at all. Any ideas on how this should be wired?
|
Posted: Monday Dec 17th, 2018 09:57 am |
|
5th Post |
Swiss-Toni
UCM Pi Users
back to top
|
I dont think you have wired that in correctly red should always be connected to + and if you are using comfort to supply power it will be to the 12V balck would go to - and on comfort com or neg, also you would need to check that comfort can handle the power requirements of the smoke alarm! if you ahve wired it back to front it will shut down your Comfort panel.....
|
Posted: Monday Dec 17th, 2018 07:48 pm |
|
6th Post |
Posted: Monday Dec 17th, 2018 08:50 pm |
|
7th Post |
Posted: Tuesday Dec 18th, 2018 03:26 pm |
|
8th Post |
Krobar
Member
Joined: | Saturday Oct 19th, 2013 |
Location: | |
Posts: | 27 |
Status: |
Offline
|
back to top
|
Hi All,
I spoke to Apollo and they said it must have end of line termination added.
The Apollo tech said a resistor needs to be in place between L1out and the spare + terminal on the PCB. As far as I can tell this puts a resistor between the + and - on the power supply.
The tech said the resistor size is determined by the alarm manufacturer.
I think this is the equivalent to 2.7K on the Hochiki diagramIf I follow the Hochiki diagram I also need a 4.7K on the zone wires (NC and C on the detector)Last edited on Tuesday Dec 18th, 2018 03:42 pm by Krobar
|
Posted: Tuesday Dec 18th, 2018 04:36 pm |
|
9th Post |
Krobar
Member
Joined: | Saturday Oct 19th, 2013 |
Location: | |
Posts: | 27 |
Status: |
Offline
|
back to top
|
Update:
Adding the 2.7K resistor between L1Out and the + terminal on the PCB made them work
They seem to work regardless of if the 4.7K resistor between NC and C is present. Is this 4.7K resistor recommended?
|
Posted: Tuesday Dec 18th, 2018 07:48 pm |
|
10th Post |
Home
Comfort Installers
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 788 |
Status: |
Offline
|
back to top
|
S12V WILL be required if you use a latching relay base....... Basically to 'unlatch' when activated.. If you use a latching base then you need a response ( triggered from a keypad shortcut key) to reset the smoke sensor.
Using the non latching base the sensor will reset itself every time it cycles its sensing.
------------------------------------
by putting the resistors into the circuit you will in effect enable a 'zone trouble' alert should anything go amiss with the cabling or set up. I,m not familiar with the apollo set up but this may mean ( for example) that a zone trouble is triggered when the head is detached from the base!
In all of our servicing and maintenance of Comfort alarms I dont think ive ever seen anybody other than ourselves use EOL for smoke alarms but its a necessity.
|
Posted: Wednesday Dec 19th, 2018 02:22 am |
|
11th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5670 |
Status: |
Offline
|
back to top
|
The is a useful connection diagram, did it comne from us?
|
Posted: Wednesday Dec 19th, 2018 08:14 am |
|
12th Post |
Krobar
Member
Joined: | Saturday Oct 19th, 2013 |
Location: | |
Posts: | 27 |
Status: |
Offline
|
back to top
|
slychiu wrote: The is a useful connection diagram, did it comne from us?
Not really; I pieced the info needed together from the comfort Hochiki diagram, the Apollo manual and a phone call with an Apollo tech.
For future reference this detector base and series works well with Comfort:https://www.apollo-fire.co.uk/products/range/series-65/relay-bases/45681-508apo-series-65-12v-relay-base
They default to non-latching and reset themselves, behaviour was perfect with the alarm sounding continuously for as long as there was smoke and resetting on its own, no need for jumper changes from default on either the detector or Comfort.
Only tested this in one detector per zone config but this wiring should work for daisy chaining too:
Comfort to Detector:Comfort +12V to Apollo PCB 12VComfort Power Com to Apollo Edge L1InComfort zone wire to NC on Apollo PCBComfort zone wire to C on Apollo PCB
Last Detector Termination:2K7 Resistor L1Out on Apollo Edge to Apollo PCB 12V (Need this for it to work at all)4K7 Resistor between NC and C on Apollo PCB (This seems to allow detection between alarm and wiring fault)
Comfort Zone set to Fire NC
|
Posted: Wednesday Dec 19th, 2018 08:16 am |
|
13th Post |
Krobar
Member
Joined: | Saturday Oct 19th, 2013 |
Location: | |
Posts: | 27 |
Status: |
Offline
|
back to top
|
Instructions attached in text format; forum keeps ruining my formatting. Attachment: Apollo Instructions.txt (Downloaded 10 times)
|
|