Can someone PLEASE just try some simple tests........ Take a working system with several UCM's Try adding another UCM and scan or removing no 2 UCM and scan - you will see what I mean.
A simple test


delete UCM 2 and do a scan, the missing UCMs will remain but in red with status Not Polled. After 10 seconds Comfigurator pops up a box 

"Possible Communications Lost or Duplicate ID for UCM/GSM ID#2. Please check the Module ID "  ie it reports the UCM #23 is a UCM/GSM in this case

 Comfigurator does not remove UCMs unless you delete the UCM from Modules.
If you add the UCM #2, Comfigurator will immediately  report

"UCM/GSM4 ID#2 Communications Restored"

After a scan the UCM ID2 in Modules will now appear in Black with status "polled" The name and ID  is unchanged

In my case UCM#1 Name was changed to UCM010 instead of UCM01. but the ID remains at 1.
Comfigurator always scans for the correct ID and displays  the ID  - it does not renumber the ID
If you change the Module ID eg from 2 to 3 and rescan, then Comfigurator will identify the new module ID eg 3, and it will assign a new Name eg UCM03.. You will lose the previous name that you assigned when it was ID2 eg Cbus, because the name was only assigned by Comfigurator and not saved in the UCM