Hi,
If DO would will give me the disired results then that\'s what I will DO.
Thanks
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi,
I tried this but it amounts to sending individual commands to the Comfort.
Let me explain in more detail as to what I am looking for.
Each lighting zone(a room) can have one or many lights, using touch screen control, when I navigate to a zone, I want to see want\'s On or Off.
To query a zone, I would like to have a response that will query specific outputs on that zone eg O?89, O?81 etc and based on the response eg OP8901/00 I can state that the Lounge light is On or OFF.
Can you look into :
1. Query an Input or Output in a Response
2. Have a Response with raw RS232 commands
Thanks
Posts: 3,493
Threads: 476
Joined: Aug 2006
Reputation:
0
Only the Y? command will give you all the outputs. Give us the Comfort and UCM version numbers to check if these will work for your system
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi,
UCM chip is 5.92
Version is FE0536222001
Y? retruns Y?0000
Comfort Ultra version 5.054
Thanks
Y?0000 would mean all outputs 1-64 are all off.
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi,
I now see where we are missing each other.
The outputs I was referring to was SCS/RIO outputs.
Any alternatives in this area ?
Please help me with this bit of confusion.
On the response page/function, I have fixed all the responses numbers I would be using via the touch screen interface. But of lately after adding more responses and downloading to Comfort, the reponses numbers are not in sync.
eg sending RS232 commands for a specific response is being executed on another response.
Any thoughts on why this might be happening ?
Thanks again
If you want the output status of the RIO outputs, you should send y? and not Y? (note the lower case character) to query.
As for the wrong response being executed, what string are you sending? Note that Comfort II Ultra has 2 byte responses, so did you send to the right response?
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Hi,
Thanks for clearing this one up, I will test and feed back.
With regards to the response numbers, I am pretty sure I am using the right code.
Take this example at one stage response number 100 was TV Room Lights, RS232 command sent is R!64.
If I look at my response table now, Tv Room Lights shows up fixed in response number 116
Sending R!74 is turning some other outputs on, but sending R!64 turns the Tv Room Lights on.
It would seem that the response numbers are out of sync.
Thanks
Posts: 279
Threads: 36
Joined: Aug 2006
Reputation:
0
Thanks for that, I will play around with this and feed back soon.
Would I be able to see outputs status for all of my 12 SCS/RIO\'s ?
Also,
On the response page/function, I have fixed all the responses numbers I would be using via the touch screen interface. But of lately after adding more responses and downloading to Comfort, the reponses numbers are not in sync.
Take this example at one stage response number 100 was TV Room Lights, RS232 command sent is R!64.
If I look at my response table now, Tv Room Lights shows up fixed in response number 116
Sending R!74 is turning some other outputs on, but sending R!64 turns the Tv Room Lights on.
It would seem that the response numbers are out of sync.