Threads: 14
Is there an easy way to force Comfort to send the output states to Cbus.
Reason: I have a PC running \"C-gate\" and \"Homegate\", This PC is turned off at night now to save power when it wakes up it syncs with the Cbus network but misses the Comfort derived changes as they don\'t exist .
If there were/is a command on Comfort to resend the current state of the Outputs to the UCM/Cbus2 life would be good.
Thanks in advance
Mike
Threads: 14
Thanks ChiuThat\'s what I have been doing. and it works great if everything is connected But if I have then turn the Pc off when I turn it back on the Cbus Sync works but it doesn\' give me the readings for any think that was set whilst the PC was off.It would take a change from comfort to register a Cbus change
My examples in the picture show UPS1 > 6 these are just relays to shed load. so I don\'t want to toggle them just to show what is on or offbut if comfort to send a level to Cbus that should Sync it
Julian\'s ComfortClient can read all the levels but that is just internal to that program.
Also if you look at the attachment
I have noticed that
the UCM-Cbus Status doesn\'t match the real settings in Comfort or Toolkit
UPS1 ON OFF OFF
UPS2 OFF ON ON
UPS3 ON OFF OFF
UPS4 ON ON ON
UPS5 OFF ON ON
UPS6 OFF OFF OFF
The system is working fine, but I can\'t resolve it at all
Mike
Thumbnail(s)
Threads: 885
I am not sure I understand this. The cbus group addresses and the Comfort Output states should not have anything to do with the PC being on or off. If you leave the PC on ten all the states are correct? The image in the attachment is too small to see properly
Threads: 62
08-24-2020, 08:12 PM
(This post was last modified: 08-25-2020, 05:52 AM by Ingo .)
I\'ve just tested the Output to Cbus mapping and it seems to work fine. Here is the process I followed:
1. Map Cbus Group 64 to Output 64 and write to EEPROM.
2. Saved Write Selective to Comfort (Reset)
3. Test with ComfortClient and Toolkit to verify online changes - working in realtime.
4. Close Toolkit and CGate.
5. Set Output 64 to On (O!4001)
6. Start Toolkit and Cgate.
7. During Toolkit Network Sync it updated Group 64 to 01.
Some Data:
- UCM/Cbus2 firmware 7.136
- Toolkit 1.15.5
Below can be seen that in CC I set the Output to On at 21:59:22 and then I started Toolkit and it updated Cbus at 21:59:48 during the Sync process.
[img]data:image/png;base64,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[/img]
Threads: 885
THanks for the confirmation
Threads: 14
Thanks Ingo
Can you confirm your UCM/CBUS2 Properties are the same as mine please?
Looking at SIM Option: Monitor
and
Monitor mode at reset
Thanks in Advance
Mike
Thumbnail(s)
Threads: 62
Mike,
Those two options are similar. If you\'d like, perhaps you could ask Chiu to make available this pre-release version to see if it helps. If I recall there has been some optimizations done which is still in a testing phase.
[img]data:image/png;base64,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[/img]
Regards,
Ingo
Threads: 885
09-06-2020, 07:38 AM
(This post was last modified: 09-06-2020, 07:41 AM by slychiu .)
We have found the problem with the output states in the Cbus to Comfort window
If a Cbus Group address is mapped to an Output, that means the Cbus address will control the output
eg in the program below, Cbus lighting address 32 Controls Output 22 Cbus address 33 controls Output 23, Cbus address 34 controls Output 24 on Comfort
This works correctly, the cbus addresses control the Outputs as expected.
However the Status shown in this window is wrong eg Output 23 status is shown in Output 22 position, Output 24 status is shown in Output 22.
The Output status in Comfort Registers is correct. The wrong Output status is only in the Cbus to Comfort screen.
This will be fixed in the next version along with other changes
In the screenshot below, Outpot 23 is Off, Output 24 is actually On, but the status shows and Output 23 is On and Output 24 is OFF .
Thumbnail(s)