I have an issue on site today
Just upgraded an early C2 5.xxx to latest 7.xxx
System had been working OK for 10 years - as soon as I loaded the new firmware onto the KNX UCM 7.079 I get a fire alarm triggered from UCM02 (18) clear this and a few minutes later same thing - then a panic alert from the UCM........
Looking at the UCM it reads OK from the EPROM BUT when I download to EPROM it DOES NOT WORK the screen flashes but actually nothing happens same with reset. This is confirmed by the fact that the read still contains data even after a reset !
CAN YOU PLEASE TEST THIS OUT AS IM ON SITE AGAIN TOMMOROW and need to get it fixed.
Posts: 6,027
Threads: 880
Joined: Apr 2006
Reputation:
3
When you Reset to Default in UCM/KNX2, it clears the KNX screen and properties to default, but it does not write to EEPROM. You have to do Write to KNX after a reset to default in order to write to KNX
Posts: 6,027
Threads: 880
Joined: Apr 2006
Reputation:
3
Tested with Comfigurator 3.12.15. Write to KNX and read from KNX worlksCan youdo a write and copy the Monitor IO
Posts: 807
Threads: 196
Joined: Jul 2006
Reputation:
0
OK
I have remote connection .....How do I know if the UCMKNX is 1 or 2 ?
Posts: 6,027
Threads: 880
Joined: Apr 2006
Reputation:
3
Scan for modules The module type will be seen
Posts: 807
Threads: 196
Joined: Jul 2006
Reputation:
0
OK that was a stupid question ........ its a 1 as it does not say knx2 and only has limited no of tabs
Posts: 6,027
Threads: 880
Joined: Apr 2006
Reputation:
3
Its easy to change the KNX module to a KNX2
Posts: 247
Threads: 55
Joined: Jul 2007
Reputation:
0
07-01-2020, 02:29 PM
(This post was last modified: 07-01-2020, 02:29 PM by TheMax74.)
Hi Chiu,
sorry for importunating you.
Does the UCM/KNX2 respond to READ requests coming from KNX BUS?
For example, if i map a Group Address to a Zone input and send a READ telegram to this Group Address, does the UCM/KNX2 respond with the current zone status?