Use of Counters
There are 256 Counters in Comfort Ultra. Each counter can have a value from 0 to 65535 (16 bits)
Counters can be used to count events
eg Zone Response
Increment Counter008
If Counter008 >= 3 Then
   Do Response Turn on Lights
   Set Counter008=0
EndIf
This will increment counter 8 whenever the zone is triggered, when the count reaches 3 it will  Do a Response to turn on selected lights, and reset the counter to 0
You can also Add a counter value or subtract a counter value
eg
Get Counter 5
Subtract Counter 6
Set Counter 7
This means Counter 5 - counter 6
The result is saved to another counter 7
Counters can also be used for Feedback in the Control Menu
Note that The Counter Menu does not need any words in OFF and ON action keys
In the Comfort App, counter as feedback will appear as a Slider
The slider positions correspond to counter values 0 for off (slider to the left) and 255 for full scale. the scale 0 to 255 corresponds to dimming levels for most lighting systems
Counters can also be used as a Link between different systems
For example, for UCM/KNX, KNX Group addresses can be mapped to Counter numbers. of the same Counter is mapped to UCM/Cbus, or UCM/Zwave, or IRIO functions, then if one device changes the value of the linked counter, then the other devices mapped to the same counter are also controlled by the counter value
In the example below, KNX group address 0/0/5 is mapped to a Counter in Comfort
When the KNX group 0/0/5 changes its value, eg 0 to 155,  this value is saved in the mapped Counter
Also if the counter value is changed in Comfort by a Response or from other systems, the updated value is sent to the mapped KNX group address, si it is a 2 way link
If another UCM eg Modbus element is mapped to the same Counter, then that allows one UCM to send commands to the other extrenal device and vice versa, or Comfort can control both devices by changing the counter value
The value of Counters can be viewed  and the value can be changed in Comfigurator 3/.11.12 and above
Go to Events > Counters in Comfigurator
Select the Counter on the middle pane
check the \"Show Status\" box for the counter in the right pane
The value of the Counter is seen in the Status field
To change the Counter value, enter the new value in the status field
Related Topics - Use of Counters, Flags, Outputs, Sensors http://www.comfortforums.com/forum126/4677.html