In the user menu there is a battery check facility....... if you press battery check option nothing appears to happen !
Is the battery status reported in the log?
Presumably there is no real means of monitoring anything other than the voltage and when this drops below a certain value the \"battery warning\" is triggered
Threads: 0
Battery Check immediately activates a battery test by switching off the AC supply and letting the backup battery supply power to the system for 2 minutes(default). If at any time during this test, a low battery condition is detected, the ac power will be turned on and a battery test fail report will be sent to the Monitoring Station.
Threads: 885
If the battery is good, nothing will be heard in the 2 minutes
Comfort does not measure the voltage during this time. Only if thevoltage drops below around 1.5 V will the battery warning alarm appear
Threads: 205
Ah
Well can i make a suggestion .........
Anybody using this facility would be quite rightly confused by the (non) action of comfort after pressing the battery test selection.
At least there needs to be some sort of acknowledgement that the battery test has indeed taken place!
So it may be that after 2 min comfort announces battery test OK ( or failed if it fails)
Alternatively
Does the battery check need to be there at all ( in the menu) - perhaps removing it all together would still mean that a flat battery is reported when the check is done at what ever interval is set.
ALSO the comment about battery check reporting to the monitoring station........ presumably it does not do this by default. I wonder in all of the many tens of thousands of comfort installations how many have ever had the battery fault reported to a monitoring station !
Your thoughts?
Threads: 219
..and does it write the result to the log file?
Threads: 885
The keypad battery test is to initiate an immediate battery test. Installers especially may need to do this instead of waiting for the 24 hour test if you suspect the battery is low
It would be possible to do an announcement at the end, but this may not be welcome if the automatic battery test is late at night!
The battery test is not recorded in the event log, that may tend to fill up the event log as there is one every day
Threads: 219
Why not allow the frequency (in days) to be configurable and also whether write to log is on/off via configuration
Surely I only need to test the battery once a week?
Ju
Threads: 885
The Battery Check Interval is already programmable in Security > Misc Settings up to 254 hours
However it is a requirement for alarm installations for many places to have a 24 hour battery check
Threads: 205
Actually the battery check in the menu is totally redundant. .....
As comfort by default checks the battery once a day ( and subsequently reports low battery if it is low) why would any body need to check through the menu. After 10+ hears experience as an installer I have never used thus function In order to get the max life out of a battery simply leave it until comfort auto checks an d reports
In my experience a 7Ah YUASA battery will last a min of 2 years and I\'ve known them to last up to 10 in low power consumption units.
Threads: 62
You can only reset the Low Battery warning with a manual Battery Check. If you replace a faulty battery you do a Battery Check and the error is cleared unless you leave it in the system for 24H and wait for an automated check.