Threads: 20
Hi - I have a problem with trouble condition on zone 5.
Even when I link the zone out and move the jumper towards the terminals so it knows there are no EOL, it still goes into a trouble condition.
Any ideas why? Could the zone be broken? That\'s a pain as I need it!
CG
Threads: 885
There may be an external voltage on the zone terminals or wires
Remove the wires from the zone and see if the trouble remains
Threads: 20
Thanks.
Yes, I\'ve tried that and I still get a trouble condition.
Here\'s what I\'m doing.
1. Moving jumper close to terminals so it knows there\'s no EOL resistors.
2. Putting a piece of continuous wire between the zone terminals so the zone is closed.
3. Set the zone as type doorwindow and it goes into trouble alarm
4. I set to zone type switchNO and switchNC to see if that makes any difference and still there is a trouble alarm whatever I do
I cannot see any other wires touching the terminals. Of course, zone 6 is connected to the shared common terminal as zone 5. There\'s never been a problem with the zone 6 which is a normally closed heat detector.
I have removed zone 6 and the problem still occurs.
Do you have any other ideas what it could be?
Threads: 20
Hi.
Update on this issue
If I set the zone as door window or switch NC, and the zone is left open, ie no link wire, and reset comfort , there is no trouble alarm. As soon as I close the circuit by putting a wire across the zone terminals, there is a trouble alarm.
Any ideas what this could be?
Thanks as always
Threads: 20
Hi.
The readings were as follows;
1. 0.596 volts - shunt in no Eol position
2. 1.22 volts - shunt in eol position
3. 1.22 volts - shunt totally removed
Any ideas?
CG
Threads: 885
The voltages are too low. It appears like the input is damaged.
Do you have a spare zone that you can use?
Threads: 20
Unfortunately not, I need all 64 now.
Good to know I\'m not doing it wrong though
Threads: 885
You can have a maximum of 5 slaves so total of 96 zones now
Threads: 20
But it buy a Slave just for one zone is a bit excessive!