UCMs Placement
#1
Hello,

I last installed a comfort 1 panel in 2006.  At the time, I needed to purchase a unibox to allow for the number of UCMs I was installing.  It appears that this is no longer available for purchase.

Can you confirm whether the following will fit into an Ultra 2 panel (non EN).  If not, what are the options for placement?:-

UCM 6 with ETH01

UCM CBUS

RIO1

LEM01-M2

RGR04

DM02

RLY01

Not forgetting the battery will be in there too.

Thanks
Reply
#2
The enclosure can fit one of the modules besides the transformer and battery
For the others you can purchase one or more empty EN01  which have mounting holes for 3 UCMs or 6 RLY size modulles
Reply
#3
Wasn\'t the USP of the Unibox though that you could mount a UCM at distance from the main Comfort panel and closer to the 3rd party device/systems interface?
Reply
#4
Thanks for the reply.

Space is a premium in this install. What is the length of the UCM cable to link out to the second EN01 panel?

Will the main panel fit UCM6/ETH01, LEM01-M2, RGR04 and DM02, along with transformer and battery?

Then one extra panel to house UCM CBUS, RIO1 and RLY01?

Thanks
Reply
#5
[img]file:///C:/DOCUME%7E1/LUYUNG%7E1/LOCALS%7E1/Temp/moz-screenshot.png[/img]The main panel wil only fit 1 UCM size module on the base if the Comfort PCB, transformer and battery are in
However,
RGR is mounted on the Comfor PCB itself
LEM is also mounted on Comfort PCB


The other 4 modules should fit on an empty EN01 enclsoure

The UCM can be connected to the main panel via CAT5 cable using the terminal blocks KA, KB, 12V, COM, not using the supplied white 4 way cable which is for short distances

Reply
#6
OK great. Thanks