Please note that the wiring from Comfort outputs to IR transmitters should be using twisted pairs (CAT 5 recommended)
Never use Alarm cables, which are untwisted, and never run several IR signals from several outputs within the same cable as it is possible for IR signals on one cable to be induced to a cable which is physically next to it. This may cause the IR signal to affect the device connected to the adjacent cable IF the IR transmitter is placed very close to the IR receiver of the device
Keep individual IR cables away from each other by at leat 25 mm, DO NOT run them side by side or within the same CAT 5 cable
If the IR Trsnsmitter is placed directly in contact wth the IR Reeceiver, the chances of a stray IR signal from another output causing a false IR signal to be transmitted is greater. In such situations, connect a 12V test lamp (available from Cytech) across the adjacent output which also sends an IR signal.
Never use Alarm cables, which are untwisted, and never run several IR signals from several outputs within the same cable as it is possible for IR signals on one cable to be induced to a cable which is physically next to it. This may cause the IR signal to affect the device connected to the adjacent cable IF the IR transmitter is placed very close to the IR receiver of the device
Keep individual IR cables away from each other by at leat 25 mm, DO NOT run them side by side or within the same CAT 5 cable
If the IR Trsnsmitter is placed directly in contact wth the IR Reeceiver, the chances of a stray IR signal from another output causing a false IR signal to be transmitted is greater. In such situations, connect a 12V test lamp (available from Cytech) across the adjacent output which also sends an IR signal.