- Swiss-Toni - 07-15-2021

I know this is a convoluted way of creating an alarm function using a RIO but due to an inability to lay further wiring to an out building, would it be possible to connect an output of a RIO directly to a zone in comfort or would I have to use a relay from the RIO output to create a Zero voltage contact to connect to the Zone: 
1)      Preferred sequence:  Sensor to RIO input. (secondary) RIO output to a Zone

2)      Alternative sequence: Sensor to RIO input,  (secondary) RIO output to a relay, relay to a Zone

This would be done on a Comfort  9000



- slychiu - 07-16-2021

You would need to use a relay from RIO Output to Comfort input, as RIO output when turned on doez not pull the voltage all the way to 0