Using RIO as an alarm extension! - Printable Version +- Comfort Automation/ Security System Forums (https://www.comfortforums.com) +-- Forum: Products (https://www.comfortforums.com/forum-3.html) +--- Forum: RIO (OBSOLETE - Replaced by IRIO) (https://www.comfortforums.com/forum-84.html) +--- Thread: Using RIO as an alarm extension! (/thread-5321.html) |
- Swiss-Toni - 07-15-2021 I know this is a convoluted way of creating an alarm function using a RIO but due to an inability to lay further wiring to an out building, would it be possible to connect an output of a RIO directly to a zone in comfort or would I have to use a relay from the RIO output to create a Zero voltage contact to connect to the Zone: 1) Preferred sequence: Sensor to RIO input. (secondary) RIO output to a Zone 2) Alternative sequence: Sensor to RIO input, (secondary) RIO output to a relay, relay to a Zone This would be done on a Comfort 9000 - slychiu - 07-16-2021 You would need to use a relay from RIO Output to Comfort input, as RIO output when turned on doez not pull the voltage all the way to 0 |