- mario.jr - 12-08-2020

Hello. I install the 7.183 firmware in my Comfort II Ultra. I have KP04 keyboards. The LEDs do not light up on the keyboards. When I put the day mode, through the application I see that it is in day mode but on the keyboards it continues as if it were in OFF mode. LEDs do not light up. Keyboards do not indicate. I have had to go back to the 7.153 firm although the zones in alert mode do not work well with it.
I hope they review it.
Thank you.



- slychiu - 12-09-2020

Can you send your cclx file to support@cytech.biz please


- Sota - 12-10-2020

Are there release notes for 7.183?


- slychiu - 12-10-2020

Sorry I thought there was a release note for 7,183 but it is not there. Will update soon



- Sota - 12-10-2020

Same goes for UCM 7.141. I\'ve been holding off upgrading until I read the release notes.


- slychiu - 12-11-2020

ULT 7.183 release notes are here

http://www.comfortforums.com/view_topic.php?id=5258&forum_id=79&jump_to=25557#p25557

UCM 7.141 is here: 

http://www.comfortforums.com/view_topic.php?id=5259&forum_id=81



- slychiu - 12-11-2020

Can you send the cclx file so we can look at the \"many bugs\" that you found?



- mario.jr - 01-03-2021

Hello.

I already sent you the cclx file. Sorry for the delay.

I have seen that I cannot configure partitions on KP04 keyboards. I don\'t know if that is the problem.

I wait for an answer, thank you.


- slychiu - 01-05-2021

KP04 Keypads cannot be used in Partitioned systems. You need KP04A. See http://www.comfortforums.com/forum125/4491.html
You will need to change your keypads and upgrade firmare for CM9001 to the latest in order to use partitions





- mario.jr - 01-06-2021

Hi.

I did some changes as some unused zones were on partition 3 and I have put them on partition 0. But after making sure everything is set to partition 0, I keep seeing errors in both 7.175 and 7.183 versions:
- Although I have not wasted the exit delay time, connecting the modes does not announce them on the keypad. It also does not announce the modes after the alarm is armed.
- The response that is activated when a mode is armed, before it was done as soon as the keyboard button was pressed and now it waits approximately the delay time to activate them.
- When I put a zone in alert mode it works as immediate mode, I also have this bug in version 7.153.

I go back to version 7.153 although I will continue testing.
Thanks