Hi,

I have Comfort I Ultra (Action 4.227) with UCM/CUBS (Cbus 5.66).

Would I able to use Location 6420 to 6547 to monitor Counter 1 to 127. The documentation mentions (Outside version only)


- slychiu - 01-16-2010

Note that the locations you mention are for Counter Responses.

For Ultra, the locations are not the same.
To find out what locations areused, startComfigurator 3, go to Events > Counters The locations are shown at the bottom left when you position the cursor on a Counter
eg  for Counter 0
(4960) = 0,0

This means Location 4960, 2 bytes value of 0,0 as Ultra Responses are 2 byte values unlike Pro



- Howser - 01-16-2010

[user=1]slychiu[/user] wrote:
Quote:Note that the locations you mention are for Counter Responses.

For Ultra, the locations are not the same.

Does that mean my firmware versions are not an issue? And I can monitor 255 Counters (Location 4960 -5470)?


- slychiu - 01-16-2010

Yes you can have Counters 0 to 127 for Comfort I Ultra, as you can see them in Comfigurator when you select Comfort I Ultra