Firmware 7.183 have many bugs - Printable Version
+--- Forum: Firmware History (https://www.comfortforums.com/forum-60.html)
+---- Forum: Comfort Firmware (https://www.comfortforums.com/forum-79.html)
+---- Thread: Firmware 7.183 have many bugs (/thread-5255.html)
Pages: 1 2
- slychiu - 01-07-2021
Your zone alert zone type is wrongAlarm type should be Alert not Intruder, see below screensho t. Your cclx file has Intruder instaead of Aler Alarm Type. That is why your zone alert causes immediate alarm
Quote:The response that is activated when a mode is armed, before it was done as soon as the keyboard button was pressed and now it waits approximately the delay time to activate them.
The Away Mode response is always activated when the system arms to Away Mode, not when you press the button. That is regardless of the firmware version.
If you want a response to run immediate when you press the Away btton then use the Start Arming Response in Misc Events. This has not changed since the beginning
- mario.jr - 01-09-2021
[user=1]slychiu[/user] escribió:
Quote:Your zone alert zone type is wrongAlarm type should be Alert not Intruder, see below screensho t. Your cclx file has Intruder instaead of Aler Alarm Type. That is why your zone alert causes immediate alarm
Hello.
If I configure it as you indicate, when activating the second sensor configured in alert it does not generate an intrusion alarm, but the keyboard starts to sound during the alert time and then it stops without making a call.
I\'ve tested it by putting En Type Zone in Trouble as Intruder.
I\'m lost.
- slychiu - 01-10-2021
In Non Detector Alarms you have changed the assignment of ND alarm 0 from Intruder to Alert, see below screenshot.
This causes the problem that you experienced.
Non detector alarms should not be changed, as they affect the behaviour of the alarm, unless you know exactly whet is the effect
Please revert all NonDetector alarms to the original setting. Open a new file Comfort 2 Ultra to compare the original settings.
Zone Types assignment should also not be changed unless you are very sure of what the effect will be.
This is regardless of the Firmware 7,183 or other older versions.
- mario.jr - 01-13-2021
Hi.
Exactly, changing the configuration of the Non-Detectors I have solved the problem of the sensors in alert mode. Although I do not remember having touched that configuration initially, also I do not get so many Non-detectors in my configuration or their names in that way, but at least it is already solved.
About the Responses of the alarm activations, I have solved it in another way, although I have to give it another turn. The issue of partitions has changed the concept of the alarm, but I cannot use them and it is creating some configuration problems for me, since I did not configure it for that concept at first.
On the other bugs that I have when using updates 7.175 and 7.183 I will continue investigating.
I will be writing on the subject.
Thank you.