We have not managed to establish communication between Comfort Generation Two and the EIB network:
After connecting the UCM the D4 “ERROR†(Red) is off. D1 “RDY†(Green) is on at all times while the D9 & D10 blinks as expected.
After some time (30-45 minutes ) the D4 turns on. After we disconnect and reset the UCM it goes off but then on again after some time.
Also we have not managed to send telegrams although a simple response was programmed and activated via the Control Menu. The D3 does not come on.
In addition the D2 “BUSY1†(Red) does not blink when there is an incoming telegram from a monitored Group address.
We double checked the polarity and everythings seems fine.
Thanks in advance.
|
Posted: Tuesday Nov 6th, 2007 12:12 pm |
|
2nd Post |
admin
Administrator
Joined: | Saturday Mar 3rd, 2007 |
Location: | Singapore |
Posts: | 1200 |
Status: |
Offline
|
back to top
|
D3 not blinking when you send a telegram from Comfort indicates tat there mey be an error in the setup
Can you send me the ccl file for a quick check?
|
Posted: Thursday Nov 8th, 2007 09:21 pm |
|
3rd Post |
marinoss
Comfort Distributors
Joined: | Tuesday May 30th, 2006 |
Location: | Nicosia, Cyprus |
Posts: | 36 |
Status: |
Offline
|
back to top
|
We will re-check the EIB addresses / groups and then send the ccl. What about D4?
Thanks
Marinos
|
Posted: Friday Nov 9th, 2007 01:45 am |
|
4th Post |
admin
Administrator
Joined: | Saturday Mar 3rd, 2007 |
Location: | Singapore |
Posts: | 1200 |
Status: |
Offline
|
back to top
|
D4 could be related to the EIB addressing
|
Posted: Thursday Nov 15th, 2007 05:49 am |
|
5th Post |
marinoss
Comfort Distributors
Joined: | Tuesday May 30th, 2006 |
Location: | Nicosia, Cyprus |
Posts: | 36 |
Status: |
Offline
|
back to top
|
Hi,
I have sent the ccl file by email.
Please note the following as well:
We noticed that the error LED goes on when there is a telegram on the EIB bus, i.e. when a button is pressed.
We also swapped the RED-BLACK bus wire on the UCM and it gives an error (as expected) which is the only thing that seems to work on the EIB UCM so far..
|
Posted: Thursday Nov 15th, 2007 08:43 am |
|
6th Post |
admin
Administrator
Joined: | Saturday Mar 3rd, 2007 |
Location: | Singapore |
Posts: | 1200 |
Status: |
Offline
|
back to top
|
The ccl file seems OK
Do you have another UCM/EIB which you can test?
Otherwise I suspect the EIB part of the UCM/EIB may be faulty. We can send a EIB plug in module to replace the one that you have
|
Posted: Sunday Nov 18th, 2007 09:51 pm |
|
7th Post |
marinoss
Comfort Distributors
Joined: | Tuesday May 30th, 2006 |
Location: | Nicosia, Cyprus |
Posts: | 36 |
Status: |
Offline
|
back to top
|
Hi,
Please do send a replacement part and let us have the tracking number.
Thanks
Last edited on Sunday Nov 18th, 2007 09:51 pm by marinoss
|
Posted: Thursday Dec 20th, 2007 08:21 pm |
|
8th Post |
marinoss
Comfort Distributors
Joined: | Tuesday May 30th, 2006 |
Location: | Nicosia, Cyprus |
Posts: | 36 |
Status: |
Offline
|
back to top
|
Unfortunately, we have not managed yet to implement the EIB:
We have installed the replaced EIB/UCM and we have set it up for a 3-level group address (Main Group 1, Mid Group 0 to 3 and subgroup 0-31) by setting the shunts as follows: SW8A Short, SW8B Open, SW8C Open, SW8D Closed.
When a switch within the range of above addresses (e.g. 1/1/3) is activated the D2 (BUSY1) blinks so we assume it correctly registers an incoming telegram.
The D9 & D10 blink so RS485 seems o.k.
Sometimes the ERROR LED lights up and after a while it goes off. Usually it does that when a switch is activated which is not in the range of addresses. Is this normal?
We have not managed to send a telegram. We used both WizComfor and Comfigurator to EXECUTE an EIB response but nothing. We also linked an EIB response to an Input Zone but again no telegram was sent. The D3 never blinked.
Any suggestions please?
Thanks
Last edited on Thursday Dec 20th, 2007 08:22 pm by marinoss
|
Posted: Wednesday Dec 26th, 2007 07:21 am |
|
9th Post |
ident
Administrator
Joined: | Wednesday Aug 9th, 2006 |
Location: | Singapore |
Posts: | 3493 |
Status: |
Offline
|
back to top
|
What is the firmware version of the UCM/EIB? We sent the EIB module without the UCM base board. We are trying to determine if the base board coould be faulty
When you attempt to send a telegram to EIB, please check if the D11 green led blinks. This indicates the UCM/EIB is receiving the telegram from Comfort.
D3 (BUSY2) blinks when a telegram is sent from the UCM/EIB to the EIB Bus
Also please make sure that SW8 E and F are off to select EIB Physical line 1
|
Posted: Saturday Jan 5th, 2008 07:01 pm |
|
10th Post |
marinoss
Comfort Distributors
Joined: | Tuesday May 30th, 2006 |
Location: | Nicosia, Cyprus |
Posts: | 36 |
Status: |
Offline
|
back to top
|
Sorry for the late reply below:
What is the firmware version of the UCM/EIB?
EIB 5.131
When you attempt to send a telegram to EIB, please check if the D11 green led blinks
There is no LED at the place which is marked as D11 (and as indicated by the EIB UCD pdf). There are other two Green LEDs D1 and D10 which are on.
D3 (BUSY2) blinks when a telegram is sent from the UCM/EIB to the EIB Bus
No, it was not possible to send an EIB telegram either from Comfort through programming or from WizComfort, nor we were able to trace and outgoing EIB telegram through the EIB bus monitor.
SW8 E and F are off to select EIB Physical line 1.
Confirmed. Only A and D are shorted.
Thanks