Very simple question can you use one output from a RIO01 to run 2 outputs on a RLY01H (would there be enough power from the  RIO01 to drive two relay points eg 3&4 indefitnetly or will I be forced to use 2 outputs from the RIO01 to control the outputs on 3&4)

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5595
Status: 
Offline

  back to top

There is probably enough current available from th IRIO to drove 2 coils on RLY01H, but it is better to use 2 IRIO outputs to be safe, unless you are short of outputs