I have a CM9000 with a UCM/ETH03, a UCM/Pi and an LEM01 giving a total of 24 zones on it. I also have a SEM/01C mounted in SEP01/C expansion box with an LEM03 (16 Zone module).I'm about to start a removation and I will need at least another 12 zones to cover additional windows, smoke alarms and external doors.What's my best option, I don't think I can add any more LEMs so should I get another SEM/01 or is there a better way of doing this?
Thanks!
|
Posted: Monday Oct 9th, 2023 03:25 pm |
|
2nd Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5759 |
Status: |
Offline
|
back to top
|
The only way is to get another SEM/SEP01 and an LEM01 which gives 16 zones. The LEM03 must be connected to the last SEP01 (with higher ID). since CM9001 has diferent models of LEM which cannot be connected to CM9000, I suggest that you set the ID of the new SEM01 to 1, and change the ID of you existing SEM01 (with LEM03) to 2, I hope that is not too confusing - you can check this post http://www.comfortforums.com/forum16/1470.html
Altyernately get 2 SEP01C and a LEM01B and LEM03B
|
Posted: Friday Oct 13th, 2023 12:32 pm |
|
3rd Post |
Sota
UCM Pi Users
Joined: | Friday May 3rd, 2013 |
Location: | Galway, Ireland |
Posts: | 86 |
Status: |
Offline
|
back to top
|
Thanks Chiu, I think I understand that! One other question, as I'm looking at using KNX to control heating, lighting, etc. I may want to add a UCM/KNX2. I don't think I have room for it in my current configuration, so I propose to remove my UCM/ETH03 and install the KNX board in it's place. I will still have network access to the system through the UCM/Pi.
What do you think?
|
Posted: Saturday Oct 14th, 2023 03:43 am |
|
4th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5759 |
Status: |
Offline
|
back to top
|
That should work. If you have the CM9001, the ETH03 can be plugged in to the PCB so you would not need the UCM/ETH03.
But please keep the UCM/ETH03 in case you should need it in future
|
Posted: Saturday Oct 14th, 2023 09:35 am |
|
5th Post |
Sota
UCM Pi Users
Joined: | Friday May 3rd, 2013 |
Location: | Galway, Ireland |
Posts: | 86 |
Status: |
Offline
|
back to top
|
Interesting, but I have a CM9000. If I upgrade to a CM9001 will my existing LEM01 and LEM03 work with it?
|
Posted: Sunday Oct 15th, 2023 02:41 am |
|
6th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5759 |
Status: |
Offline
|
back to top
|
If you use the OLD LEM01, LEM02, LEM03 you will have to set the shunts to Double EOL (and use the EOL resistors). You will not have the option to have No EOL
|
Posted: Monday Oct 16th, 2023 10:40 am |
|
7th Post |
Sota
UCM Pi Users
Joined: | Friday May 3rd, 2013 |
Location: | Galway, Ireland |
Posts: | 86 |
Status: |
Offline
|
back to top
|
OK, that's not a problem as all my zones have double EOL resistors.
|
|