Hi Chiu
currently, when mapping comfort zones to KNX Group Addresses, 0 = Off, 1 = On.
Is it possible, to allow the user to invert the values sent to the bus: 0 = On, 1 = Off ?
Thanks
Massimo

Last edited on Thursday Feb 13th, 2020 01:42 pm by TheMax74

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

If you use Physical zone mapping to KNX you cannot change the meaning of 0 for off, 1 for on. That is the universal meaning of 0 and 1. One would not normally associate 0 for on and 1 for on
However if you use Zone Responses to send KNX telegrams then you are free to send any KNX telegram for each zone on and zone off event

TheMax74
Member


Joined: Monday Jul 16th, 2007
Location: Italy
Posts: 247
Status: 
Offline

  back to top

Hello Chiu.
Good idea. Thank you.
With Voice Assistants like Alexa, Siri, Google home, the mapping must be 0 = On, 1 = Off.
Bye.

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

I think someone should tell them that they have done it wrongnobody things 0 for on 1 for off

TheMax74
Member


Joined: Monday Jul 16th, 2007
Location: Italy
Posts: 247
Status: 
Offline

  back to top

Hi Chiu.
I spoke with an Apple Homekit developer about that.
It makes somewhat sense.
Contact Sensor device type (in all 3 voice assistants) bring the zone value as is.

If the contact is closed, the zone is INACTIVE (like in Comfort), therefore for these 3 assistants, the zone is secure and they represent that with "Off" (that means "no problems")

If the contact is open, the zone goes to ACTIVE, therefore for these 3 assistants, the zone is unsecure and they represent that with "ON" (that means "hey, there is a problem here").

For now, i solved by unmapping Zones from KNX/UCM and by using the UCM/PI to do an inversion of the zone values, but you'll find out having same issues like this one, as soon as some Comfort installer will try to link KNX zones with the voice assistants.

;-)

Last edited on Friday Feb 14th, 2020 01:04 pm by TheMax74

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Comfort zone types can be Normally Open or Normally Off
If you want contact Closed to be Off and Open to be On, the you select a Normally Closed Zone Type eg Switch Normally Closed


Hence yoiu do not need to make amyu special zone responses, just map input to KNX dorectly