Posted: Sunday Dec 15th, 2019 05:21 am |
|
1st Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5495 |
Status: |
Offline
|
back to top
|
Comfigurator 3.12.12
Known Bugs- Slave RS485 Communications Failure is displayed wringly in the status bar as Door station ID #-15. But pop up message Slave Communications Failure ID#1 is correct.
- Actions Set and Clear Counter (Action 158) have reverse effect. Set should be set to 255, Clear should be clear to 0
- KNX/Logic Action send to KNX uses invalid ID (shoukld be 1). Do not use KNX actions for KNX/Logic
- KNX/Logic - if UCM/GSM4 is connected, Comfigurator will give exception after scanning
- Old BUG- The "OR" condition in a Response is incorrect after a Read from Comfort (old bug)
Bugs Fixed- TSM, MSM, HIO after scan, latest version was Unknown
- Fixed bugs on MSM -Default for "Water Leak Sensor Change Report" is wrong. After "Read from EEPROM", always switch to "MSM01 Properties" tab . Input 4 settings are not updated after "Read from EEPROM"
- When IRIO Digital zone mapped to Virtual Input – the Zone Reference to IRIO was not seen
- Output status in Comfort Registers > Output status. For Check status function When Output status changes the Output status in check stutaus is off by 1. when output is changed using the Output status window the status is correct
- Some computers had exception when Comfigurator is started - "System.NullReferenceException: Object reference not set to an instance of an object at Comfort.KP04A.get_EnableFlagNameSen1()) "
New Features- Velbus configurator supports configuration file .cfgx so new velbus modules can be added in future without a new Comfigurator version
- Options > settings> UCM Connections – add Connect button so connection can be tested on the same screen
- Supports UCM/Pi detected in Modules Scan
- Supports new KNX/Logic Controller
- Improved Vocabulary matching. Comfigurator detects the Vocabulary type programmed in Comfort and forces the wordlist to the correct Vocabulary to avoid mismatch in word lists betwen Comfigurator and Comfort
- Improved detection of Comfort firmware and File System, and improved File conversion between file systems
- Controllers with built in UCMs show the UCM properties in the Controller Tab (eg CM9001, LGX01, UCM/Logic, KNX/Logic)
Last edited on Saturday Mar 28th, 2020 04:37 am by slychiu
|
Posted: Sunday Dec 15th, 2019 05:22 am |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5495 |
Status: |
Offline
|
back to top
|
Comfigurator 3.12.13 (Beta)
Known bugs- KP04AT Internal Temperature sensor field Read froom KP04 is not correct, does not update the sensor
- Cbus Custom application 1 and 2, when Read from Cbus EEPROM, values of FF give exception.
- Divide Action 157 shows Wring Parameters in Response Wizard
- Old BUG- The "OR" condition in a Response is incorrect after a Read from Comfort (old bug)
Bugs Fixed from 3.12.12- Action Code Counter clear and set 158,0 and 1 were reversed
- KNX/Logic – when UCM/GSM4 is connected, scan gets exception
- UCM/Logic add UCM give exception (not connnected to system yet)
- Slave 1 comms failure is reported as Door station -15 in status bar
- When connecting to a Comfort with a different vocabulary from the cclx file, Comfigurator detects the vocabulary correctly, but when selecting words, the wrong wordlist is used (according to the cclx file, not Comfort). However after saving the file and opening again, the correct vocab is used
- KNX/Logic gets exception when UCM/GSM4 was connected
New Features and Changes- UCM/Modbus – allow different modbus id on each Modbus to Comfort line.
- Added Action 160 s12V timed off to turn off S12V for programmed duration. (requires New Comfort Firmware to be released)
- Added Subtract action 149, 3 subtract Immediate Action. (requires New Comfort Firmware to be released)
- Added Set user partition action 161 (requires New Comfort Firmware to be released)
- Ucm/Pi module tab added virtual input assignment. If UCM/Pi is already in the configuration, delete and add it again to see the new Virtual Inputs tab
- CM9001- EMS Sensors calibration allow decimal fraction (requires New Comfort Firmware to be released)
- KP04AT temp sensor - KP Internal Temp Sensor field for KP04AT with temperature sensor
- C-bus 2 custom applications 1 and 2. Requires new UCM/CBUS2 Firmware (to be released)
Last edited on Saturday Mar 28th, 2020 04:37 am by slychiu
|
Posted: Sunday Dec 15th, 2019 05:22 am |
|
3rd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5495 |
Status: |
Offline
|
back to top
|
Comfigurator 3.12.15
Known Bugs- In Phone Numbers, when UCM/GSM4 is in the systrem, the Phone Permission checkboxes are missing for each user. They are enabled by default for all users
- Old BUG- The "OR" condition in a Response is incorrect after a Read from Comfort (old bug)
Bugs Fixed
- KNX/Logic send text to id=01 (self) was invalid. This allows Status on bottom left to work
- Divide action Parameters are fixed
- In the Zones screen when the "Status " checkbox is checked to show the real time state of zones, when a zone state changes, the screen goes back to the top so higher numbered zones could not be seen easily. Now this has been improved so the zones screen does not jump when any zone state changes.
New Features/Changes- IRIO 0-10V Dimmer Input switch added parameters "Direction" and "Quick Press" so that the switch can be used to dim up and dim down by long opress
- IRIO analog outputs 0-10V added mapped on/off flag which turn off when the analog output value is 0 and turn on value is > 0. This flag controls an output which can be used to switch the analog output on or off
- UCM/Cbus2 : When Imported from CBZ, the Register assignment is not changed in Comfigurator if already mapped to Comfort Counter, Flag, Virtual Input etc. If a new Group address is imported, it is Unassigned (ie FF)
- Register Monitor Window. This is a new window that allows selected Inputs, Outputs, Counters, Flags, and Sensors to be monitored for real time value. However, an issue is that new file will also ask to log in, even when there is no register defined.
- UCM/GSM4 added new 4G type 3 = 7600-LTE to support future LTE module
Register Monitor
The new Register Monitor feature is very useful when you want to monitor a range of Comfort registers; Zones/Inputs, Outputs, Counters, Flags, and Sensors. Before this, you had to go to Zones to monitor zones, Outputs to monitor outputs, Counters to monitor counters, etc. This new feature allows all required registers to be monitored in a single window.
Go to Comfort Registers > Register Window.
The Login window appears. Enter a valid user code.
A new window appears "Add Register to Monitor"
Select Counter, Flag, Output, Sensor or ZoneThen select the register number according to the register type selected
Continue adding registers to the monitor window.
The real time status of the Registers are shown
Last edited on Saturday Mar 28th, 2020 04:37 am by slychiu
|
Posted: Thursday Feb 20th, 2020 08:16 am |
|
4th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5495 |
Status: |
Offline
|
back to top
|
Comfigurator 3.12.16
Known Issues- Read From GSM4 EEPOM does not update Time Update for LTE
- Subtract sensor from last action causes error
- Old BUG- The "OR" condition in a Response is incorrect after a Read from Comfort (old bug)
New Features- New menu Transfer > WRITE Comfort to UCM EEPROM copies Comfigurator EEPROM to the UCM EEPROM for backup. This is equivalent to pressing and holding the UPLOAD button in the UCM Requires UCM 7.131. see http://www.comfortforums.com/forum20/5159.html
- New Menu Transfer > READ Comfort from UCM EEPROM restores the backup from UCM EEPROM to Comfort - This is equivalent to pressing and holding the DLOAD button on the UCM Requires UCM 7.131
- Changes in UCM/gsm4 for LTE
- Action 27 Motion Detect action to be assigned to Zone ON and Zone Off Response. In Misc Events a new parameter Occupancy Time determines the duration in minutes for which no motion in the affected zones will indicate as "No Ooccupancy". dR01 message means Occupancy, DR00 means No occupancy
Last edited on Tuesday Apr 14th, 2020 07:13 am by slychiu
|
Posted: Sunday Sep 5th, 2021 05:37 am |
|
5th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5495 |
Status: |
Offline
|
back to top
|
Comfigurator 3.13.7 - 1 September 2021
Known Bugs- Action - Virtual Input On/Off - if no virtual Inputs, selects zone 1 as virtual and changes zone 1 to Virtual.
- Action - Virtual Input On/Off. If there are virtual Input Virtual Input On/Off can see the correct Virtual Inputs but cannot select the correct zone- Zone 1 is selected
- Modbus Slave Addresses – display of addresses is wrong- Please ignore or see the document Modbus Slave Addresses for the correct slave addresses to poll
Bugs Fixed- After converting the file system from ULT to OPT, If Register Monitor was monitoring an outpu not supported by OPT, an exception was seen.
New Features- If Last Action Value accepts 2 bytes and negative valuies, same as if Counter value
- UCM/Modbus Properties – added Poll cycle delay in 50 ms units
- UCM/Modbus Slave Addresses Display allow new modbus addresses (Bit there is an error in the save addresses display)
- File > Import for Infrared .ifr files, Configuration Items, Scenarios will browse to their default folders to ease searching for the correct items
Comfigurator 3.13.7 can be downloaded from http://www.cytech.biz/comfigurator.html
Last edited on Friday Dec 10th, 2021 05:32 am by slychiu
|
Posted: Sunday Dec 18th, 2022 03:24 am |
|
6th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5495 |
Status: |
Offline
|
back to top
|
Comfigurator 3.13.9- Fixed Bug – Modbus Slave addresses for Bypass Inputs were not corrected
- Fixed Bug The KNX/Modbus EEPROM write had an issue with the comment text for the Modbus->Comfort failing to write
- Fixed Bug IRIO properties is that maximum setpoint can go lower than minimum setpoint. Although there are checks implemented, they fail when up and down buttons are used.
- ISM09 default temp offset reporting should be 0 not 1
- USB drivers have been updated in C:\Program Files\Cytech Technology\Comfigurator\USB Drivers
Known Bugs- The action Set Virtual Inputs On/off is able to select a virtual input to turn on or off
- If UCM ID=1 is not connected, scanning for Modules using ETH03 plugged in to the CM9001 or UCM with ID 2 onwards, the UCM Module will show ID1 Firmware 255.255 OTHER see http://www.comfortforums.com/forum20/5435.html
Last edited on Sunday Aug 6th, 2023 02:20 am by slychiu
|
|