slychiu Administrator
|
If you hear this message when trying to arm the system, there are two possibilities;
|
|||||||||
rooster2001 Member
|
i couldnt find a action table on prog thats why i couldnt reset as u said engineer reset |
|||||||||
slychiu Administrator
|
No you do not need an actyion code to reset You need to sign in using the Engineer code F0 6789# OR if you had an arm failure, just disarm the system again Either one of these will clear the message |
|||||||||
Stephen Coates Member
|
I have this problem, but cannot solve it using any of the suggestions. |
|||||||||
slychiu Administrator
|
Do you have a battery connected? If not the system does not allow you to arm, as under reguations, battery disconnected is considered as low battery |
|||||||||
Stephen Coates Member
|
thanks. No I don't. Sorry. |
|||||||||
slychiu Administrator
|
If you do not have a battery connected, then you may have a Battery Warning Alarm. You normally are not able to arm the system with a Low battery active This is a setting that can be changed in Modules and Settings > Configuration Flag > Allow Low Battery to Arm Reset after changing the setting |