We have an existing installation that we have recently upgraded for the customer. The set up was using a UCM with an RS232 daughter board to connect to a centralite system.
After upgrading the UCM to 7.XX there appears to be no communication out of the UCM.
When an RS232 communication is sent...- There is a flashing LED on the main board L10 L11 - NO flashing LED on the UCM D9 and D10
Am I correct in saying that the LED's D9 and D10 should flash when an RS232 communication is sent?
|
Posted: Monday Mar 18th, 2019 11:23 am |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
D9 and D10 flash when there is communication woth Comfort on the RS485 busIf D9 and D10 are not blinking there is no comms with ComfortD11 and D12 are for communications with Rs232
|
Posted: Monday Mar 18th, 2019 07:56 pm |
|
3rd Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
More to the point it was working BEFORE i upgraded to 7.XX form 5.XXX
Are you able to test this with a 7.XXX version?
|
Posted: Tuesday Mar 19th, 2019 03:05 am |
|
4th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
Can you send the cclx file to
edit
"support@cytech.biz" Last edited on Tuesday Mar 19th, 2019 04:17 am by slychiu
|
Posted: Tuesday Mar 19th, 2019 11:56 am |
|
5th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
The cclx file is OK. Upgrading from UCM v5 to v7 should not affect it.
The Responses to send mesages to Centralite should work (but whether the commands to centralite work is not known because we do not have any centralite here).
You said that D9 and D10 were not blinking, is that the case? if so then the ucm is not being polled, and that does not have anything to do with the firmware or programming.
If that is fixed, then when you send a command to Centralite, the D11 (Red) LED (NOT D9) should blink meaning that a message is being sent to the Rs232 interface.
Another suggestion not related to this issue. The programming UCM should always be at UCM ID 1 and any other interface UCM should be ID 2 or more. This is because for UCM ID1 can be removed from the network without causing a Communications Failure alarm. UCMs at other IDs when removed will cause Comms failure alarm
|
Posted: Wednesday Mar 20th, 2019 10:37 am |
|
6th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
Centralite
Were you aware that they are no longer manufacturing Centralite litejet or the larger version.... think they went into receivership a couple of years ago.
We do have software if anyone is in trouble OR can be upgraded without tooo much hassle to KNX.
|
Posted: Wednesday Mar 20th, 2019 11:52 am |
|
7th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
I think they were announcing new products in dec 2018 si i would be surprised if they went into receivership
|
Posted: Wednesday Mar 20th, 2019 03:01 pm |
|
8th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
so i have a test rig set up
mimics the file i sent you
on UCM1 (the centralite UCM) ( RS232 daughter board in place but NO RS232 'load") D11 D12 DO NOT flash when I send an RS232 command.
Howeveron UCM2 (the network UCM) D11 D12 DO flash when I send an RS232 command.
Does the RS232 command get sent universally to all boards and only flashes if it sees an RS232 handshake (even though the response is addressed to only a SINGLE UCM !).
|
Posted: Thursday Mar 21st, 2019 02:36 am |
|
9th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
The RS232 command gets sent only to the UCM that is addressed.
Your results indicate that you have mixed up the addresses of the UCM 1 and 2.
I suggest yiou scan for modules, check which is centralite, check the response and write to Comfort That will sort out the problem
|
Posted: Thursday Mar 21st, 2019 07:33 am |
|
10th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
My results may indicate that BUT I've DOUBLE checked.
The leds on the UCM2 flash when i send a Centralite response which is directed to UCM1.
I am using the file i sent you.
Are you able to replicate the scenario.
I still have set up on bench -
|
Posted: Thursday Mar 21st, 2019 07:34 am |
|
11th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
the only thing i dont have is somethng on the end of the RS232 daughter board BUT surely the LEDs should blink even if there is nothing to deliver to !
|
Posted: Thursday Mar 21st, 2019 08:54 am |
|
12th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
It appears that you are correct. The later UCM firmware does block the send text message if that UCM is not logged in.
A new UCM firmware will fix that
The UCM Universal is the UCM of choice when communicating with 3rd party systems as it allows different baud rates for communications
|
Posted: Thursday Mar 21st, 2019 12:15 pm |
|
13th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
YES ! YES! YES!I'm finally correct!
No great rush but any idea when the update will be available?
Thanks
|
Posted: Thursday Mar 21st, 2019 12:17 pm |
|
14th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
Universal - again agreed and again I'm aware of - HOWEVER this is an existing installation and already programmed by original installer.
|
Posted: Friday Mar 22nd, 2019 05:19 am |
|
15th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
Testing now, maybe about 2 weeks after all the ISO9001 procedures are fullfilled
|
Posted: Tuesday Mar 26th, 2019 03:24 pm |
|
16th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
Any progress on this yet?
|
Posted: Tuesday Mar 26th, 2019 03:24 pm |
|
17th Post |
Home
Comfort Distributors
Joined: | Wednesday Jul 12th, 2006 |
Location: | United Kingdom |
Posts: | 771 |
Status: |
Offline
|
back to top
|
Any chance of a beta release?
|
Posted: Wednesday Mar 27th, 2019 02:10 am |
|
18th Post |
Posted: Wednesday Mar 27th, 2019 08:26 am |
|
19th Post |
Posted: Monday Jul 15th, 2019 08:03 pm |
|
20th Post |
darnold
Member
Joined: | Thursday Feb 26th, 2009 |
Location: | United Kingdom |
Posts: | 20 |
Status: |
Offline
|
back to top
|
I just came across this post. I have a very similar problem in that my UCM/RS232 board connected to my Dynalite Gateway stopped working when sending Comfort -> Dynalite messages but works fine Dynalite -> Comfort.
Should I try this beta version?
|