 New Topic   Reply   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Monday Nov 19th, 2018 05:03 am
   PM  Quote  Reply 
1st Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

http://www.arduinostarterskit.com/sale-7641832-lightweight-four-channel-relay-module-for-arduino-red-board.html

I am trying to wire up my Comfort Output to my 4 channels Relay to switch on the light in the event of PIR is being activated. Refer to above link for details of my 10A 250V relay. How do I connect the output and 12v from Comfort panel to the relay input?

Q1 Is it correct to connect the 12V of the Output to DC+ of the relay module?
Q2 then connect the OP1 of the Ouput to IN1(Input 1 ) of the relay? And accordingly OP2 to IN2 and so on?
Q3 How about the DC- of the relay? Where to connect to or leave it unconnected?

Would appreciate your support and sharing.

Last edited on Monday Nov 19th, 2018 05:04 am by david8811



 Posted: Monday Nov 19th, 2018 06:05 am
   PM  Quote  Reply 
2nd Post
Swiss-Toni
UCM Pi Users


Joined: Thursday Sep 15th, 2011
Location: Greater London, United Kingdom
Posts: 349
Status: 
Offline

  back to top


Last edited on Monday Nov 19th, 2018 06:11 am by Swiss-Toni



 Posted: Monday Nov 19th, 2018 12:51 pm
   PM  Quote  Reply 
3rd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

I would guesss that you need to set low level trigger option and connect Comfort Output to the trigger inputThen connect 12V to positive wireBut that is only a guess



 Posted: Tuesday Nov 20th, 2018 12:57 am
   PM  Quote  Reply 
4th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

May I know why you suggested Low level trigger setting? Was it because Comfort output is designed for Low level trigger? Another way to put it. Is Comfort output Control signal is programmed/set to Low level trigger or to activated at 0 / false / ground, when an output signal is generated ( in my case ,PIR is activated)?

Last edited on Tuesday Nov 20th, 2018 06:08 am by david8811



 Posted: Tuesday Nov 20th, 2018 11:39 am
   PM  Quote  Reply 
5th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

The Comfort Output is an Open-collector transistor output. That means that when not activated the output is floating.When an Output is turned on, the Comfort Output will go to a low level, thus supplying 12V between 12V and Common. Hence it is activve low level
This is designed to drive 12V relaysIf you were using the RLY01, yiu would not have this problem. The outputs can be coonnected direct to the relay inputs pin for pin



 Posted: Tuesday Nov 27th, 2018 10:56 pm
   PM  Quote  Reply 
6th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

Thank you for your response.
I read in another blog, the DC- terminal is supposed to be connected to the Arduino panel Ground terminal. In my case, which one is the “Ground” terminal of Comfort panel?

See the link here

https://blog.siliconstraits.vn/relay-what-is-it-and-how-to-use-it/

Last edited on Tuesday Nov 27th, 2018 10:58 pm by david8811



 Posted: Wednesday Nov 28th, 2018 01:30 am
   PM  Quote  Reply 
7th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

The Ground can be found in Comfort 12V/COM/S12V centre terminal



 Posted: Wednesday Nov 28th, 2018 02:27 am
   PM  Quote  Reply 
8th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

I just tested my relay by connecting the DC+ and DC- of the relay to the +ve and -ve poles of my 12V 20A 240W (18 channels) DC external power supply. Set the Relay to Low Level Trigger. Then I connected the relay output 1 to a light bulb with external 240V AC power supply. When I connected (jumped) the Relay Input 1 to DC- terminal of the Relay, the Relay activated and the light on.

Now, I intended to power up my Relay using external power supply to reduce the loads to my Comfort system power supply. To do this, I connect my Relay DC+ and DC- to the +ve and -ve poles of my 12V 20A 240W (18 channels) DC external power supply. Similarly, the Relay ouput1 to a light bulb with 240V AC power supply.

To enable Comfort system to activate the Relay and switch on the light when my PIR sensor is activated, I will connect my Relay Input 1 to my my Comfort OP1 (Output1) terminal. Leave the 12V “free” unconnected as my Relay is drawing power from the external DC supply as explained above.
Q1 . Will this configuration work? If yes, Do I have to connect my Comfort system Ground (COM) to the -ve pole of my external 12V 20A 240W (18 channels) DC external power supply to create a common ground?

PS : The 12V 20A 240W (18 channels) DC external power supply is also used to power up 8 units of my NVR cameras

Last edited on Wednesday Nov 28th, 2018 02:56 am by david8811



 Posted: Wednesday Nov 28th, 2018 02:58 am
   PM  Quote  Reply 
9th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

Yes you need to connect the ground of the power supply to the ground for Comfort (centre of 12V/COM/S12V terminal)



 Posted: Tuesday Dec 11th, 2018 02:36 am
   PM  Quote  Reply 
10th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

Mr Chiu,

http://www.cytech.biz/temp/appman.pdf
I am trying to set up the project : Switch on a light when movement is detected at night as per above link example 1.4. ( This example used OP5, I changed the programming from OP5 to OP3)
I tested the circuit as per your suggestion, Unfortunately it didn’t work. Then, I reconnected the Relay power supply directly to Comfort panel, which is DC+ to 12V between OP3 and OP4. The DC- to COM between S12V and 12V. With DC+ and DC- connected, the Relay green LED on indicate power on.

When I connected the Relay Input IN3 to Comfort OP3, the Relay immediately activated and the light connected to the Relay output was lighted up. The Relay activated without the PIR being activated. Furthermore, the Relay continued activated and failed to switch off despite this project Response is programmed to 5 minutes.

When I disconnected the IN3 cable from Relay to OP3, the Relay deactivated, but the Relay remained power on. When I reconnected the IN3 cable to OP3, the Relay activated again, light on and failed to switch off. Despite PIR is not even activated.
I also tested the above based on Zone type 5 and 24. Same result. Zone type 8 ( despite the example used zone type 8) cannot be used as it caused F32 to announce the zone.
Would appreciate if you could help to address my problem.

Last edited on Tuesday Dec 11th, 2018 03:09 am by david8811



 Posted: Tuesday Dec 11th, 2018 05:12 am
   PM  Quote  Reply 
11th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

It is very difficult to check what you have done without a cclx file
The Output 3 may be On  but you may have some other event which causes it to turn on
we also cannot verify that you have programmed correctly
There is also the problem whether your connection of the relay to the light is correct


the Relay deactivated, but the Relay remained power on. When I reconnected the IN3 cable to OP3, the Relay activated again, light on and failed to switch off.

"relay deactivated but relay remain power on " does not make sense
we cannot advise properly, I suggest you get an electrician to help.

Last edited on Tuesday Dec 11th, 2018 05:17 am by slychiu



 Posted: Tuesday Dec 11th, 2018 11:56 am
   PM  Quote  Reply 
12th Post
John W
UCM Pi Users
 

Joined: Wednesday Feb 18th, 2009
Location: United Kingdom
Posts: 107
Status: 
Offline

  back to top

David, break it down into two parts: the comfort config, and relay wiring.

To check you have got the comfort output switching properly you can stick a meter between the output and 0v, or better still an led between 12v and the output with a resistor to current limit it.
e.g. https://www.laser.com/product_info.php/item/LP01-Comfort_Test_Lamps_12v/cPath/96_162/products_id/930
That will prove you have the output switching on when you want it to.
If you are using Comfigurator you can actually watch the output status change, so you can see if it is on or off easily.


Wiring wise, The relay board you are using has configurable switch inputs using the jumpers. Have you got them set for triggering high or low ?
Will it accept an open collector 'input', and does it have an integral pull-up resistor to pull the input high itself, or does it need an external one.

I would test it as follows:
This assumes using 3rd relay/channel being used.

Mains side: live feed to 'comm3', output to light to 'NO3' (normally open).

DC Side: DC+ to positive supply, DC- to negative supply.

With nothing connected to the input, turn the DC power on. Does the relay close or not ?
Ideally it shouldn't do.

Set the jumper to trigger low.
Connect a wire to 'IN3' and connect it to DC-. This should turn the output on. If it has internal pull-ups when you disconnect the wire from DC- it should turn off. If you find this doesn't happen reliably it probably means the input is floating (no pull-up) and needs say a 10k ohm resistor between IN3 and DC+ to pull it high.

----
To connect to the comfort panel:
DC+ to positive supply (12v on comfort pcb), DC- to negative supply (comm next to it).
Comfort OP3 to the relay board IP3.

I hope that is of some help.



 Posted: Wednesday Dec 12th, 2018 02:03 am
   PM  Quote  Reply 
13th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

Hi John,

Thank you for your response.
My wiring circuit is exactly what you suggested. I also did the test you suggested i.e connect and disconnect IN3 with DC-, the Relay was activated and deactivated accordingly. It concluded that Relay is working perfectly.
Objective: Comfort turn on light ( connected to OP3) if the time is between 7 pm to 6am. The light will be turned off after 5 minutes if no further movement is detected. Similar to the example 1.4 of application manual. Refer the link above.

I had actually at the next stage of the problem. I have wired my PIR to zone 17 with zone type 24 with Response 45 On.

Response 45 action codes are as follow:-
73, 3, 69, 19, 70, 6, 193, 74, 5, 194, 1, 1, 44, 6, 255.
To test it, I changed my Comfort system time to 8pm. When I walked past the PIR, the PIR activated the relay and the light switched on. The problem is, the Relay and of course the light would not deactivated or switches off after 5 minutes.

I changed Response 45 5 minutes interval time to 5 seconds with Action Code 73, 3, 69, 19, 70, 6, 193, 74, 5, 194, 1, 0, 5, 6, 255. Similar result as above. It can only be turned off when I reset the Comfort system reset button. It appaeared that Response 6 to turn off Output 3 is not activated. When I measured the volatage across DC+ and IN3, the voltage remain 12V.

I am using Comfort 2 system whereas the example in 1.4 of Application.manual is for Comfort 1. Not sure they are compatible. I read in Action Codes manual page 60, couldn’t find any issue so far.

Would appreciate your help.

Last edited on Wednesday Dec 12th, 2018 03:21 am by david8811



 Posted: Wednesday Dec 12th, 2018 06:43 am
   PM  Quote  Reply 
14th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

your Response 6 is supposed to turn off the output
You need to check what is response 6 action
Do you have Comfort 2 Optimum or Ultra?

Last edited on Wednesday Dec 12th, 2018 06:54 am by slychiu



 Posted: Wednesday Dec 12th, 2018 08:26 am
   PM  Quote  Reply 
15th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

Response 6 Action codes is default setting, which are 128, 3, 0, 255.

I just reconfirmed the action codes for Response 6 a while ago. My Comfort System Control Number obtained from Engineer Menu 743 is 743361. Not sure it is Ultra or Optimum

Last edited on Wednesday Dec 12th, 2018 10:46 am by david8811



 Posted: Wednesday Dec 12th, 2018 10:50 am
   PM  Quote  Reply 
16th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

If you have programmed everything correctly then it should work
We are not able to check for you as you are not able to save the cclx file so you wil have to check all the responses yourself, with a good understanding of actions and responses
Check the action codes manual as a start
http://www.cytech.biz/action_codes_reference.html
make a control menu to turn on and off the output



 Posted: Wednesday Dec 12th, 2018 12:13 pm
   PM  Quote  Reply 
17th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

For Comfort Ultra
194, 01, 00, 05, 107, 03 Start Timer 1, count = 5 seconds, and Do Response 875 (3 x 256 + 107)

Above statement is from Comfort Action Codes Manual, page 60. It says For Comfort Ultra, .....What is the last action code 03 means? There are 6 action codes here compared to mine is only 5 action codes. Could it be I missed something here as my Comfort is ultra I Guess.



 Posted: Wednesday Dec 12th, 2018 12:21 pm
   PM  Quote  Reply 
18th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top


Action Code: 194
Parameter 1: Timer 1 to max
Parameter 2: timer count high byte - Seconds/256 (0 to 254)
66
Parameter 3: timer count low byte - remainder Seconds (0 to 254)
Parameter 4: Response 00 to 255
Parameter 5: Response High Byte for Comfort Ultra only.
The Timer value in seconds is entered in action codes 3 and 4 (16-bit value)
194, 01, 00, 05, 107, 03
Start Timer 1, count = 5 secondResponse = 3 x 256 + 107 = ???



 Posted: Thursday Dec 13th, 2018 03:03 am
   PM  Quote  Reply 
19th Post
david8811
Member
 

Joined: Wednesday Aug 15th, 2018
Location:  
Posts: 23
Status: 
Offline

  back to top

Hi Chiu,

Q1 Can you explain to me the difference between timer 1, 2 or 3? Are these timers need to be preprogrammed?

Q2 From Action Codes Manual, Page 60. “Avoid 255 in the Response high byte and low byte as this will terminate the Response entry.”
What is that means?

Last edited on Thursday Dec 13th, 2018 03:28 am by david8811



 Posted: Thursday Dec 13th, 2018 11:35 am
   PM  Quote  Reply 
20th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

Please see this topic about timers
http://www.comfortforums.com/forum92/4062.html