Comfigurator 3.11.1
Known Issues
  1. Writing to EEPROM for UCM/KNX writes  empty data, so the group addresses mapping is lost
  2. For Selective Read for any comfigurator item, if the referenced Response is not present in Comfigurator responses, then the response becomes Null. eg If Time Program references Response 100, and Comfigurator does not have this response, then the Time Program response becomes Null Response. Selective Read should be done only for information purposes. A Full Read from Comfort is needed to know the correct program in Comfort. (old bug)
  3. For Graph References, if there are any references to HIO and TSM modules (new unreleased modules), an un-handled exception is seen
  4. In IRIO, any input function after selecting  the Register Type (eg Couter, Flag), is not able to select the Register Number (Counter or Flag number). The workaround is to go to another Input or screen and come back to the input to select the Comfort register.
  5. For KT03 using Counters and Outputs, the Counter and Outputs Reference to KT03 is not shown in blue in the Counters page and Outputs page (old bug)
  6. When the cclx file wordlist does not match the vocabulary (Voice) in Comfort, logging in to Comfigurator will change the wordlist to the one in Comfort, but the words selected in Zones and Control menu are still the wrong wordlist and the words written to Comfort will be the worng  wordlist . To work around, the Wordlist in Comfigurator must be changed manually to the one on Comfort before doing a write to Comfort (old bug)
  7. Reading from Comfort does not read the Daylight Saving table into Comfigurator (in Sunrise/Sunset Times), although the Sunrise/sunset times are read. (old Bug)
  8. If  UCM/Cbus2 is present, all zones are referenced to UCM/Cbus2 because of the Cbus2 Physical Inputs, even though the Physiacl Inputs are not mapped to Cbus (old Bug)
  9. In Flags, if Check Status box is checked for a flag, the status is updated, but if the flag changes subsequently, the flag status in the centre pane is not updated until you go to another page and back, or uncheck and check the box (old bug)
Bugs Fixed
  1. Read from Comfort  removed all the Modules from the modules tab
  2. Register References for TSM and HIO were not shown. However now Graph References causes exception.
  3. For IRIO "Show References" did not include the "Summer/Winter Flag Name"
  4. For IRIO, ISM07 Relay I/O, Blinds DC had "Unhandled exception" error when clicking on Pulse width. After changing Pulse Width or Min Pulse Gap, the properties of the submodule cannot be changed.
  5. For IRIO, Read from IRIO always has Travel time = 254 seconds
  6. In Control Menu, after selecting Feedback Types = Output, Flags or Zones/Inputs, the words for 0 = Off and 1 = On are automatically entered. This works correctly now.
New Features
  1. Support for new UCM/KNX2 with enhanced KNX Interface. UCM/KNX2 is still being tested and is not released yet.
  2. Graph References hover remains on for 30 seconds (instead of 10 seconds) so it is easy to read the Responses.
  3. For IRIO, the control and feedback registers have been changed. Control/Feedback Register combines the main Control and Feedback register into one register so that the user does not need to specify a separate control register and feedback register if they are the same. 3 other control registers allow scenes
  4. For IRIO, each Submodule properties window shows a summary of the assigned Outputs and Inputs Functions without having to select each Output/Input to find out the Function assigned
  5. In the Control Menu, if Feedback Type = Output, Zones, or Flag is selected, the action Keys 0 and 1 are automatically entered as Off and On respectively. This saves time in programming the Control Menu especially for use in the Comfort app. In a future Comfort firmware upgrade, pressing the Off and On buttons wil automatically cause the Flag, Output to be turned on or off.  However the "Off" and "On" words  cannot be seen in the Control Menu unless you go to another page and come back to it.

Last edited on Sunday Jul 29th, 2018 01:31 pm by slychiu



 Posted: Sunday Jul 29th, 2018 01:18 pm
   PM  Quote  Reply 
2nd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Comfigurator 3.11.2
Known Issues
  1. In Flags screen, if Check Status box is checked for a flag, the status is updated, but if the flag changes subsequently, the flag status in the centre pane is not updated until you go to another page and back, or uncheck and check the box (old bug)
Bugs Fixed (from 3.10.11)
  1. Comfigurator 3.10.11 could not install on Windows XP.
  2. File > Update Defaults did not work in 3.10.11. 
  3. In Zwave, after doing a Learn from Zwave, Flag mappings were changed into Counter in Zwave Mappings.  This bug was in older versions of Comfigurator as well.
  4. Virtual Node in Zwave Configurator  Virtual Node Info - SEND button n the right pane was missing from Comfigurator 3.10.9
  5. IRIO Get status did not work
  6. For KT03 using Counters and Outputs, the Counter and Outputs Reference to KT03 is not shown in blue in the Counters page and Outputs page (this is an old bug)
  7. When the cclx file wordlist does not match the vocabulary (Voice) in Comfort, logging in to Comfigurator will change the wordlist to the one in Comfort, but the words selected in Zones and Control menu are still the wrong wordlist and the words written to Comfort will be the worng  wordlist . To work around, the Wordlist in Comfigurator must be changed manually to the one on Comfort before doing a write to Comfort (old bug)
  8. Reading from Comfort did not read the Daylight Saving table into Comfigurator (in Sunrise/Sunset Times), although the Sunrise/sunset times are read. (old Bug)
  9. If  UCM/Cbus2 is present, all zones are referenced to UCM/Cbus2 because of the Cbus2 Physical Inputs, even though the Physiacl Inputs are not mapped to Cbus (old Bug)
New Features & Improvements
  1. In the Control Menu, if Feedback Type = Output, Zones, or Flag is selected, the action Keys 0 and 1 are automatically entered as Off and On respectively. This saves time in programming the Control Menu especially for use in the Comfort app. In a future Comfort firmware upgrade, pressing the Off and On buttons wil automatically cause the Flag, Output to be turned on or off.  This is a real time-saver for the Comfort apps.
  2. Graph References hover remains on for 30 seconds (instead of 10 seconds) so it is easy to read the Responses.
New Modules Supported
  1. Supports new IRIO Automation Module and submodules
  2. Supports new UCM/KNX2 3rd generation KNX Interface.



 Posted: Sunday Jul 29th, 2018 01:19 pm
   PM  Quote  Reply 
3rd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Comfigurator 3.11.3
Known Bugs
  1. Actions for UCM/KNX2 are wrong. Use flags and counters instead to send telegrams to KNX
  2. In Flags screen, if Check Status box is checked for a flag, the status is updated, but if the flag changes subsequently, the flag status in the centre pane is not updated until you go to another page and back, or uncheck and check the box (old bug)
  3. Importing a Configuration Item from a file with a different file system causes exception (old bug)

Improvements
  1. IRIO submodules selection are listed in Alphabetical order, ie ISM01, ISM02...
  2. IRIO Added Temperature Sensor Function function to submodules ISM01, ISM07. This requires an external TSM01 Thermistor and allows mapped sensor to rad the temperature.
  3. IRIO added Resistive Sensor Function to submodules ISM01, ISM07. This caters for any resistive type  sensor eg Light, Pressure etc to be mapped to sensor.
  4. IRIO Added IR with Feedback Function to ISM03 Infrared submodule which uses  Current sensor as feedback for the IR controlled device
  5. IRIO current sensor function added Mapping to Sensor as additional to  Flag so the Sensor can be used to determine the current sensing level
  6. In UCM/Cbus2, when adding Group addresses the group address can changed so it does not need to add  in sequence from low to high
The IRIO changes require IRIO firmware 7.004 see http://www.comfortforums.com/forum129/4460.html



 Posted: Sunday Jul 29th, 2018 01:21 pm
   PM  Quote  Reply 
4th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Comfigurator 3.11.6

Known Bugs
  1. If Input does not work for Input > 64 to 96. This also applies for older versions
  2. Deg C /deg F in Comfiguration flags is incorrect
  3. Optimum when adding  UCM/KNX2 causes exception
  4. Read from KP06A or KP04A does not change the KP06A/KP04A settings  in Comfigurator
  5. IRIO IR codes do not refresh when new IR codes are learned. Refresh button is needed
  6. Default template def40.cctx for UCM/Logic is missing from the installation. Please do File > Update Defaults to update the set of  default templates.
  7. In Flags screen, if Check Status box is checked for a flag, the status is updated, but if the flag changes subsequently, the flag status in the centre pane is not updated until you go to another page and back, or uncheck and check the box (old bug)
  8. Export Scenario does not work. Selecting any items will cause an exception
Bugs Fixed
  1. Actions for UCM/KNX2 did not work
  2. Importing a Configuration Item from a file with a different file system causes exception (old bug)
  3. Known Bugs in HIO and IRIO have been fixed
New Features
  1. Support for 4 Partitions in Comfort (requires Comfort Firmware 7.110)
  2. In Security > Zones, each zone has new settings for Partition and EOL shunts. These are for future Comfort features
  3. Support for UCM/Logic in File > New

Last edited on Sunday Jul 29th, 2018 01:25 pm by slychiu



 Posted: Sunday Jul 29th, 2018 01:25 pm
   PM  Quote  Reply 
5th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Comfigurator 3.11.11

These are the changes from Comfigurator 3.10.6

Known Bugs
  1. Cannot install on Windows XP. Windows XP users do not upgrade to this version. Windows 7 or above only for this version
  2. File > Update Defaults does not work. This should update the default configurations and templates. To work-around, please unzip the files from this link http://www.cytech.biz/download_files.php?item_id=843 and save in the Comfigurator Installation folder. You do not need to exceute the files
  3. In Zwave, after doing a Learn from Zwave, Flag mappings are changed into Counter in Zwave Mappings.  However this does not afffect the actual mappings in UCM/Zwave, only the display in Comfigurator.To workaround, do another Read from EEPROM for Zwave. This bug was present in older versions of Comfigurator
  4. Virtual Node in Zwave Configurator  Virtual Node Info - SEND button n the right pane is missing from Comfigurator 3.10.9 
Bugs Fixed
  1. Scan for SCS/IRIO detected RIO as IRIO
  2. Inserting "Else" in a Response between If and EndIf  caused Exception
  3. Fixed Read from Comfort Exception when iRIO is present
  4. UCM/CBUS2 Limit of concatenated bytes is limited to 17 so that there is no overflow. Previous versions limited it to 18 bytes which is too much.
  5. In KT03 where write to KT03 failed to any reason, the message "KT03 Upgrade timed out" was changed to "Write/Read to KT03 Timed out"
  6. In KT03, if a button has a status for Zone > 64, read from KT03 caused the zone to be blank.
  7. Fixed BUG. After Module scanning, KP06 and KP04A modules which are removed from the system were not shown. They should be shown in red with the status "Not Found". Only Modules with properties in memory eg UCM/KNX, KP06, KT03 etc will be shown as Not Found. Modules that do not have saved properties will not be shown at all in the modules list if they are removed from the system.
  8. UCM/eHomegreen fixed scanning for modules problem where the scanned modules were not seen.
  9. For Logic Engine without voice, the warning that Vocabulary does not match before write to Comfort has been removed
New Features and Changes
  1. Support for IRIO
  2. Scanning for Modules has been speeded up greatly. What took up to 1 minute now takes only a few seconds, due to a new  scanning method. This requires Comfort Firmware 7.093. Older firmware will still use the old scanning method. This is especially useful as more module types are added to Comfort which would increase the scanning times otherwise.
  3. Timers (in Names > Timers) has a field  called  Timer Status. The "Show Status" button will show the Timer as OFF or ON, and if ON, the remaining timer in seconds is displayed. This is a useful tool when programming and testing Timers.           
  4. "Clear Event Log" button has been added to the Event Log window. It is good practice to Save the event log and delete it so that old events are not lost    
  5. In System Information, "Vocabulary Number" eg 5, has been changed to "Vocabulary Name" eg "English Residential"
  6. The Action "Send RS232" applies to all UCMs, not just the general UCM, so that new commands can be sent to other UCMs which are not supported before.
  7. Send RS232 action in Hex mode accepts space as separator between bytes as well as comma
  8. In Comfort Registers, show Status, clicking on the Status will change the value for counter, sensor  ir toggle for Flag

Last edited on Monday Nov 11th, 2019 05:41 am by slychiu



 Posted: Sunday Jul 29th, 2018 01:28 pm
   PM  Quote  Reply 
6th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Comfigurator 3.11.13
Comfigurator  3.11.13 has the following changes

Known Issues
  1. IRIO- ISM03 - Input Function Current Sensor mapped to Comfort Sensors - Sensor references are not shown or displayed in Blue
  2. IRIO - ISM07 - Input Functions Analog Input and Resistive Sensor mapped to Comfort Sensors - Sensor references are not shown or displayed in Blue
Modbus Configurator
  1. For Comfort to Modbus, the Comfort registers for Discrete Inputs added Output, Output Toggle, Output Pulse, Virtual Input, Counter, Sensor, Flag, Arm, Panic, Bypass zone.  Discrete Inputs and Input Registers now have the same Comfort register types
  2. Comfort Registers for Coils and Holding Registers are the same, ie Physical Input, Counter, Flag, Sensor. Holding Registers added Physical Inputs, Flags
  3. In Modbus to Comfort, when Comfort register is mapped to Modbus, the Show Status Box allows the Comfort register eg Counter, Flag to show the real time value (allowing the comfort register changes due to modbus to be seen), and allows the value of the register  to changed in the status box (allowing the effect in Modbus Registers to be tested).
Upgrade Firmware by UCMJ Programming Cable
  1. For the process of upgrading firmware by UCM programming cable, when the upgrade fails or succeeds, the message "Scan for Modules Yes/No" at the end has been  removed. This is because Scan for modules does not work while UCM programming cable is connected, and the message leads to users attemting to scan for modules and failing

Alternative Phrases on Control Menu
  1. In previous Comfigurator versions,  we can enter alternative phrases in Control Group, Control Key and Control actions.However if the Phrase words are empty, the Control menu does not show the group, key or action and they appear as empty.Alternative Phrase is now displayed in the Control menu list if the phrase words are empty. In fact even if there is both alternative phrase and Phrase words, the Alternative Phrase should take precedence. This is to make it easier to create the control menu when the voice menu is not needed eg for the comfort apps or for Logic Engine LGX01 and UCM/Logic which do not have voice

HIO

Added Properties for
  1. Doorbell Occupancy Hold Time,
  2. Window A/C Off Dim Level 1,
  3. Window A/C Off Dim Level 2
  4. Occupancy Off Dim level 1,
  5. Occupancy Off Dim level 2
IRIO
  1. Relay I/O added Input Function Analog Input
KT05
  1. Added new Keypad type