gfoden Member
|
I have a comfort alarm installed with peripheral sensors and PIRs and a ZWave board. It works well. I have as well, another BMS with ZWave and need to communicate between them. For alarm state e.g. day, night, away etc. I pick up the state in Events/Miscelaneous events/day mode partition 1 and set a response to set a Zwave register to a value. (off=0), day=10..etc.) The other BMS treats the register as a dimmer and polls the state every minute. It works a treat and the other BMS knows what security state the house is in. (It took a while to understand the hidden range conversion from 1-255 to 1-99!) I would like to be able to signal the state "that the alarm had been triggered" to the other system but can't find an event driven response that I can program to set the ZWave register in comfort to 100 say. Could someone explain how I do it please? Geoff |
|||||||||
slychiu Administrator
|
You can create an Alarm Response for Intruder AlarmMake a new Response for UCm command, Zwave Action Basic set Command and set the level to 100 to the Zwave Address You would have to reset this to 0 when the System is disarmed, using the System Disarmed Alarm Type Response |