Sorry if this is a daft question, I think it is but as its being discussed on another forum thought I'd best check here.
1) is there any issue with wiring up shock sensors to comfort, and can standard sensors be used ? What settings do you use ?
|
Posted: Thursday Dec 28th, 2017 04:51 pm |
|
2nd Post |
Swiss-Toni
UCM Pi Users
back to top
|
they are either NO or NC circuits it should go straigt in with either setting they work in the same way as a PIR or door contact.....
Ps their is no such things as a daft question, knowledge all started from questioning!
Last edited on Thursday Dec 28th, 2017 04:53 pm by Swiss-Toni
|
Posted: Thursday Dec 28th, 2017 04:56 pm |
|
3rd Post |
wexfordman
UCM Pi Users
Joined: | Monday Jan 1st, 2007 |
Location: | Cork, Ireland |
Posts: | 546 |
Status: |
Offline
|
back to top
|
Thanks Tony,
So the settings are pretty much in the zone settings where you would slect the sensitivity for the shock sensor ? Don't have access to clmfigurator at the moment so can see the options for zone type
|
Posted: Thursday Dec 28th, 2017 04:57 pm |
|
4th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
If the shock sensor has a processor, it should have a dry cocntact like a PIR so normal settings for zone like door/window can be used
if it is a raw vibration sensor which has very fast transitions then you need a very fast sensitivity setting, see the Vibrartion zine type
|
Posted: Friday Dec 29th, 2017 07:45 pm |
|
5th Post |
wexfordman
UCM Pi Users
Joined: | Monday Jan 1st, 2007 |
Location: | Cork, Ireland |
Posts: | 546 |
Status: |
Offline
|
back to top
|
slychiu wrote: If the shock sensor has a processor, it should have a dry cocntact like a PIR so normal settings for zone like door/window can be used
if it is a raw vibration sensor which has very fast transitions then you need a very fast sensitivity setting, see the Vibrartion zine type
Hi slychiu,
There is a discussion in an IOT forum where I was mentioning ck fort and ST integration, but some of the users are querying as to whether comfort is suitable as an alarm system and his it handles shock sensor's, which I am not familiar with.
So perhaps you could clarify how comfort handles shock sensor's, as many are saying that it would require an external analyser board to do it correctly ?Can you define both Gross and Pulse parameters for shock sensors to monitor for both types of attack?
Could you also link to comfort standards etc so I can link to them in the forum ?
https://touch.boards.ie/thread/2057750838/4/#post105671816
|
Posted: Saturday Dec 30th, 2017 06:20 am |
|
6th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
That link does not work
Shock sensors or vibration sensors detect vibration
Those with a processor will analyse the vibration amplitude and duration and determine if it is a real "shock"
Those without processors give contacts but they will switch on and off very rapidly, and are prone to false alarms, eg a slight tap may cause it to trigger
For comfort to process these select the Vribraton zone type which has sensitivity = 20 ms so it can detect the transitions, but use a Zone Response Vibration Analyser in Default Responses. This makes an alarm if there are 3 activations within 30 seconss
|
Posted: Saturday Dec 30th, 2017 04:21 pm |
|
7th Post |
OhPinchy
Member
Joined: | Wednesday Dec 27th, 2017 |
Location: | |
Posts: | 33 |
Status: |
Offline
|
back to top
|
Hi, repasting link to the Boards.ie thread here https://www.boards.ie/vbulletin/showthread.php?t=2057750838.
I am user FrankGrimes on that thread and am considering purchasing Comfort (based on excellent advice from wexfordman).
Alarm installers on that thread are highlighting a potential deficiency in Comfort vs standard alarm panels (in Ireland HKC is most prevalent player): HKC alarms allow both Gross and Pulse settings to be configured:
If a single large blow is detected above the acceptable Gross level, the alarm will sound (e.g. set it high enough to ignore wind, but low enough to detect a hammer strike).
If a single blow is below the acceptable Gross level, but is followed by further soft blows (below Gross level) within a certain timeframe, then the alarm will sound. This is controlled by the Pulse setting and being able to configure it is important for avoiding false alarms caused by recurring gusts of wind etc.
Assuming we are talking about shock sensors without inbuilt processors (as one imagines it’s more time consuming to trial-and-error test these by having to walk to each one and adjust settings on it directly e.g. by dip switches):
1. Can Comfort detect and differentiate between Gross and Pulse attacks?
2. Can the thresholds for both these type of attacks be configured in the Comfigurator software?
3. Is any additional hardware (e.g. a separate shock sensor analyzer board) required to provide this functionality (and if so, what hardware is recommended)?
Rather than try interpret whether your previous response addresses the above, it would be great to avoid any possible ambiguity: I hope the answers confirm this functionality is provided by Comfort as this will help ensure it is regarded as on par with the main alarm panels in Ireland (and is then strongly differentiated by its fantastic automation capabilities). Since becoming aware of it, both my electrician/alarm installer brother-in-law and close friend builder are very interested in learning more and possibly adopting it in their jobs - I reckon the more people find out about how powerful it is, the more adoption there will start to be in Ireland. And I’m very much looking forward to getting to grips with it myself! Thanks
|
Posted: Saturday Dec 30th, 2017 06:37 pm |
|
8th Post |
Swiss-Toni
UCM Pi Users
back to top
|
I have not wired in a tremblor sensor for years as not often called for these days, however it will still come down to the type of vibration sensors that you use. I cannot see any reason why Comfort system would not be able to handle a vibration sensor of any kind as with any sensor they all work on either a open or closed signal and with intelligent system it will determine vibration level setting before triggering, I think you would need to look at the vibration sensor you want to use and then ask SLYCHIU if it is comapatable (probably would be) and what settings to enter when programing that particular zone.
Or ask if anyone has used that particular sensor on the forum and what settings they used and for any issues surrounding it.
|
Posted: Sunday Dec 31st, 2017 09:52 am |
|
9th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
OK, it seems that HKC does claim "analyser" capability in every zone
However given that the panel inputs accept Open/Close contacts, the analysis capability is limited to measuring the duration and count of pulses, and not the actual strength or amplitude of the vibration.
In that case both Gross and Pulse count settings can be achieved with Comfort, although not under those names.
"Gross" level can be handled by the Zone Type sensitivity setting, from 20 ms to 800 ms (7 levels), is the duration of the activation. Lower values are for higher sensitivity and higher values for lower sensitivity.
Pulse count can be handled by the Vibration Analyser Response eg 3 counts in 30 seconds (both parameters can be changed) in the response. Hence Comfort gives fine tuning of the pulse count and timing compared to those which have fixed levels of pulse count like HKC.
These settings are useful when used with low cost vibration/shock sensors which have a ball and cup design and do not have inbuilt analysers
There are also many other shock sensors with analysers eg https://firesecurityproducts.com/product/intrusion/GS620BN/61841
From that link, it describes exactly how Comfort handles it except Comfort has another adjustable variable of 30 seconds for the pulse counts
"The analysing capability has two separate detection criteria: gross attack and pulse count. The gross attack threshold is designed to react to a single blow, while pulse count alarms when a pre-selected number of smaller shocks, occuring within a 30 second timing interval is reached. Both detection levels can be adjusted so that the installlation can be fine tuned to the environment and fully tested using the walk test facility. This digital signal processing is designed to eliminate false alarms and assure reliable detection of all types of attacks."
Comfort can be used with either type of sensor.
Last edited on Sunday Dec 31st, 2017 09:57 am by slychiu
|
Posted: Wednesday Jan 3rd, 2018 04:04 pm |
|
10th Post |
OhPinchy
Member
Joined: | Wednesday Dec 27th, 2017 |
Location: | |
Posts: | 33 |
Status: |
Offline
|
back to top
|
Thank you very much slychiu for the comprehensive response. That makes it clear that the gross and pulse attack detection I need is provided for by Comfort. I will move ahead with ordering the Comfort equipment shortly and look forward to getting to use it.
I will consider what type of shock sensors I go for and if there is any doubt about compatibility will return to seek clarification, though it sounds like it's quite likely any sensor I go for will be covered. Thanks again
|
Posted: Wednesday Jan 3rd, 2018 04:40 pm |
|
11th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
I am confident these settings will handle almost all sensors of this type. I have personally been on site with installers where the window grill frame was very large, so that a light tap can set off the sensor, to small and rigid plates where you need a large bang. The sensitivity setting and count allows you to cater for both extremes
Comfort is not quite as easy as a normal alarm system to set up, but let uis know if you have problems
|
Posted: Saturday Nov 16th, 2019 10:09 am |
|
12th Post |
palmlodge
Member
Joined: | Thursday Dec 14th, 2006 |
Location: | United Kingdom |
Posts: | 507 |
Status: |
Offline
|
back to top
|
I'm installing some shock sensors, a couple of questions. The sensor is a Texecom Impaq S and has options I need to configure. Can you advise what I should be selecting for Comfort, and would I need to use a resistor?
Thanks
Attachment: shock 1.png (Downloaded 60 times) Last edited on Saturday Nov 16th, 2019 10:10 am by palmlodge
|
Posted: Saturday Nov 16th, 2019 10:11 am |
|
13th Post |
Posted: Sunday Nov 17th, 2019 01:24 am |
|
14th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
I believe the Alarm should be 4K7 and the Tamper should be 2K2
Attachment: Dbl_EOL.png (Downloaded 58 times)
|
Posted: Saturday Nov 23rd, 2019 10:42 am |
|
15th Post |
palmlodge
Member
Joined: | Thursday Dec 14th, 2006 |
Location: | United Kingdom |
Posts: | 507 |
Status: |
Offline
|
back to top
|
I've come to install, and now not sure so what to connect. The connections on your diagram won't align to what is on the shock sensor itself.
Do I use resistors both at the Comfort panel AND at the shock sensor?
Can I ignore the tamper? If the intruders are in, PIRs will sort out the alarm, these shocks just need to trap external factors.
Do I take the zone output to the shock sensor to EOL1, then loop a 4k resistor to EOL2, and then the common from EOL2 back to the Comfort panel perhaps?
Thanks!
Attachment: texecom impaq s.png (Downloaded 53 times)
|
Posted: Monday Nov 25th, 2019 03:34 am |
|
16th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
You can conect the EOL resistors either at the sensor end or at comfort, not at both
The DIP switches seem to indicate that the sensor has internal resistors, but I canot confirm without seeing their circuit diagramMaybe you need to do some trial and error
|
Posted: Thursday Dec 5th, 2019 09:15 am |
|
17th Post |
palmlodge
Member
Joined: | Thursday Dec 14th, 2006 |
Location: | United Kingdom |
Posts: | 507 |
Status: |
Offline
|
back to top
|
I presume I just do the following?
-Connect the Comfort zone output to one of the EOL connectors on the shock
-Connect the Comfort zone common to the other EOL connector on the shock
-Select option 2 on both the shock DIPs for the resistance required by Comfort which is 4K7 alarm, 2K7 tamper.
-Then something on Comfort to tell it there's an EOL connection rather than a regular PIR style connection?? I looked here but it wasn't clear to me http://www.comfortforums.com/forum127/4935.htmlLast edited on Thursday Dec 5th, 2019 09:17 am by palmlodge
|
Posted: Thursday Dec 5th, 2019 11:16 am |
|
18th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
You should just go ahead and try it, as I do not know what they mean without the actual internal circuit
In Comfort, make sure the EOL shunts are moved away from the terminal block
Go to Security Check mode by Keypad F,3,2.
If there is no zone trouble announced then it is correct/ Open the zone, the zone should be announced, not zone trouble
Pres F to end the mode
|
Posted: Tuesday Jun 30th, 2020 11:12 am |
|
19th Post |
palmlodge
Member
Joined: | Thursday Dec 14th, 2006 |
Location: | United Kingdom |
Posts: | 507 |
Status: |
Offline
|
back to top
|
I tried, and failed. I can power these shocks, but cannot get Comfort to detect any data.
Is there a way I can send a unit at my cost to Cytech, or someone in the UK, to test and confirm what's needed to make them work?
Thanks
|
Posted: Tuesday Jun 30th, 2020 12:28 pm |
|
20th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
Yes send it over, I have given my address by emailinclude any instructrions
|