I might be swapping out my door station for a new VOIP video one (probably am) 
I currently use the door station to make a momentry connection to my gates to open them.
Assuming this goes - Do I need a relay?  Or can I just use one of the OP connections straight off the board?  In my case it would be the slave in the garage.  (Either way, how do I work out which OP it is to programme in Comfigurator?)
My gut feel is is I will need a little relay....
Thanks
Stuart

Last edited on Wednesday Dec 6th, 2017 09:07 pm by schford

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

You need a relay to provide dry con tacts. The Outputs are open -collector

If you have a DM02 with the DS01 door station, there are 2 relays in there. Otherwise use RLY01 or separate 12V relay

Use the Open Door Response or Open Gate Response to activate any response to pulse any outputs on Comfort or slave

schford
UCM Pi Users
 

Joined: Wednesday Feb 25th, 2009
Location:  
Posts: 248
Status: 
Offline

  back to top

thanks have ordered along with new eth03 :-)