I might be swapping out my door station for a new VOIP video one (probably am) I currently use the door station to make a momentry connection to my gates to open them. Assuming this goes - Do I need a relay? Or can I just use one of the OP connections straight off the board? In my case it would be the slave in the garage. (Either way, how do I work out which OP it is to programme in Comfigurator?) My gut feel is is I will need a little relay.... Thanks Stuart Last edited on Wednesday Dec 6th, 2017 09:07 pm by schford |
|||||||||
slychiu Administrator
|
You need a relay to provide dry con tacts. The Outputs are open -collector If you have a DM02 with the DS01 door station, there are 2 relays in there. Otherwise use RLY01 or separate 12V relay Use the Open Door Response or Open Gate Response to activate any response to pulse any outputs on Comfort or slave |
|||||||||
schford UCM Pi Users
|
thanks have ordered along with new eth03 :-) |