Posted: Tuesday Jun 6th, 2017 04:49 pm |
|
1st Post |
eborges
Member
Joined: | Tuesday Apr 27th, 2010 |
Location: | Portugal |
Posts: | 9 |
Status: |
Offline
|
back to top
|
Hello
I have 21 motion detectors connected to Comfort and during normal house activity it causes a lot of traffic on the KNX bus and delays on the transmission of information from Comfort to KNX.
I would like to skip the sending, from Comfort to KNX, of the status report for the motion sensors but still receive information of the non-motion sensor zones.
Is there a way to selectively report zone status to KNX bus ?
( by the way in the 'UCM/KNX2 - Comfort to KNX Interface' pdf manual in page 27 it is referred "In the screen shot above, the zone status is assigned to Group address 0/1/1." but there is no such screenshot . Please correct manual)
Regards
Eurico
|
Posted: Tuesday Jun 6th, 2017 05:28 pm |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5498 |
Status: |
Offline
|
back to top
|
It looks like you may be using in Alarms to KNX > Zones status
This will report all the zones in Comfort to KNX sequential group address
Disable this, and use the Inputs to KNX tab instead. Here you can select those Inputs/zones that you want to map to KMX group addresses
We will check the manual. thanks for feedback
|
|