In Properties, select Modbus Master/Slave as Master
If Modbus Interface is TCP, then the Comfort Server Manager link will be shown
Tabs: Modbus to Comfort, Alarm to Modbus, Monitor Mode can be seen
Modbus to Comfort
This is applicable for UCM/Modbus as Master only, not as Slave.
In this tab, the Modbus addresses are defined and mapped to Comfort registers (Counters, Flags, Sensors, Outputs, Arm Security, Panic, Bypass Zones). Up to 256 Modbus addresses can be mapped to Comfort
A Typical Modbus to Comfort screen is shown above. Press Add Modbus Element to add another element
Select the Modbus Element Type from - Discrete Input
- Coil
- Input Register
- Holding Register
Discrete Input
Modbus Discrete Inputs are 1 bit (on/off) registers that can be mapped to Counters, Virtual Inputs, Flags, Outputs, Output Toggle, Output Pulse, Arm Security, Panic, Bypass Zone
Coil
Modbus Coils are 1 bit (on/off) registers that can be mapped to Counter, Physical Input, Counter, Flag , Sensor
Input Register
Modbus Input Registers are 16-bit registers that can be mapped to Counters, Sensors, Flags, Outputs, Virtual Inputs, arm security, panic, bypass zone. Modbus Input registers are read only, and cannot be changed by the maped counter and sensor.
Holding Register
Modbus Holding Registers 16-bit registers can be mapped to Counters, Physical Input, Flag, Sensors, Modbus Holding registers are read/write registers and can be changed by the mapped counter and sensor.
Modbus Register Number
After selecting the Modbus element (Coil, Discrete Input, Input Register, Holding Register), enter the Modbus Address in Decimal or Hexadecimal notation (depending on the setting in Properties). Modbus Registers have a range from 0 to FFFF Hexadecimal or 0 to 65535 in Decimal.
Avoid entering the same Register number for the same Modbus element type, eg Coil 1000 is entered in the table it should not be duplicated in any of the tables to avoid conflict. Every Modbus device will have a table showing the Modbus element and address and the function related to it, so that other Modbus devices acting as Master can read and/or write to the correct Register.
Number of Registers
This means that multiple modbus slave registers can be polled in one command. For example in the above screenshot example on the 1st line, Modbus address 0 Discrete Input and mapped to Flag 21. No of Registers = 5 means that 5 sequential Modbus registers are mapped to 5 sequential Flags.
eg - Modbus address 0 -> Flag 21
- Modbus address 1 > Flag 22
- Modbus address 2 > Flag 23
- Modbus Address 3 > Flag 24
- Modbus Adress 4 > Flag 25
These modbus addresses must be the same type eg Discrete Inputs
This allows the Modbus Master to poll the slave very fast and reduces the number of Modbus to Comfort Table entries. The above example required 5 entries before, but nopw only requires 1 entry in Modbus to Comfort
Last edited on Sunday Sep 25th, 2022 03:02 am by slychiu
|
Posted: Tuesday Jan 31st, 2017 01:53 pm |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
Comfort Register Mapping
Modbus Registers can be mapped to Comfort Registers. The following Comfort Register Types are described below
Counter
Modbus 1-bit (Discrete Inputs, Coils) are either On or off. Map to Counter means the Modbus Input state Off sets the mapped counter value to OFF and Modbus Input On sets the counter value to 255. The Counter Response (if assigned) is triggered. This allows the Modbus Discrete Input state change to cause a Response to be executed. The Response can check the counter value,
eg If Counter 001 = 0 then .
Do this
else
Do that
endif
Modbus Holding and Input Registers are 16 bit registers that can be mapped to Comfort Counters. The 16 bit value from Modbus is written into the mapped Counter register.
Modbus Holding Registers and read/write, and any change in the mapped Comfort counter is also updated to the Modbus Register.
Modbus Input Registers are read only, so changes in Comfort Counters are not updated to the Modbus Register.
Virtual Input
When a 1-bit (On/Off) Modbus register (Coil, Discrete input) is mapped to a Virtual Input, the Modbus register can act like an alarm Input which can cause an alarm when armed, Select a Zone/Input which is not used otherwise. The zone/input can be any unsed zone, even when it is not physically on Comfort or Slave, eg Comfort with only 16 zones, Virtual Input can be on any unused zone from 1 to 16 or >16. When a zone is a virtual input due to mapping by Modbus discrete input, the physical input will not work.
Flag
When When a 1-bit (On/Off) Modbus register (Coil, Discrete input) is mapped to a Flag, the state of the Flag will follow that of the Modbus element On or Off.
Output
When When a 1-bit (On/Off) Modbus Discrete Input Register is mapped to an Output, the state of the Output will follow that of the Modbus Element On or Off.
Select Output number.
Output Toggle
When a 1-bit (On/Off) Modbus Discrete Input register is mapped to an Output Toggle, the state of the Output will toggle ie invert state when the Modbus Element turns on.
Select Output number.
Output Pulse
When a 1-bit (On/Off) Modbus Discrete Input register is mapped to an Output Pulse the state of the Output will Pulse on for 1 second when the Modbus Element turns on.
Select Output number.
Arm Security
When a 1-bit (On/Off) Modbus register (Discrete input) is mapped to Arm Security, the security system will arm to the security mode when the Modbus Element turns on. Select the Security Mode to arm to (Away, Night, Day, Vacation).
Panic
When a 1-bit (On/Off) Modbus register (Discrete input) is mapped to Panic, the Modbus element Input will trigger a Panic Alarm when turned on.
Bypass Zone
When a 1-bit (On/Off) Modbus register (Discrete input) is mapped to Bypass zone, the Modbus element Input will bypass the zone when turned on and unbypass when turned off.
Select a Zone/Input.
Note
Comfort Registers cannot be duplicated in the Modbus to Comfort table. For example you cannot map the same Counter to 2 Modbus registers
Comments Field
Enter maximum 16 characters in the comments field to describe the Modbus register. This field has no function and is saved in the UCM/Modbus EEPROM so it can be read back to show optional information.
|
Posted: Tuesday Jan 31st, 2017 01:55 pm |
|
3rd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
Alarm To Modbus
This is applicable for UCM/Modbus as Master only, not as Slave.
This is for signalling of Alarm conditions to Modbus. Map the alarm condition to a Modbus element for notification of alarm conditions.
The alarm conditions are listed below;
- Zone Not Ready (1 bit): Zone Open during arming
- Arm state: Off (disarned), On (armed)
- Alarm state: Off (No alarm), On (full alarm). Trouble, alert is not alarm.
- Panic: Panic alarm
- Tamper: Tamper alarm
- Line Cut: Phone Trouble/Line Cut
- AC Failure: Power /AC Failure
- Arm Failure: Failed to Arm
- Low Battery
- Alarm Type: see Alarm Types in Comfigurator > Security Types
- Security Mode: 0=Security Off, 1=Away, 2=Night, 3=Day, 4=Vacation
- Alarm Zone: Last zone which caused alarm
- Alarm User: User armed and disarmed
- Alarm RS485 ID: Communications Failure Module ID
- RS485 Comms fail: Communications Failure state
- Bypass: Zone Number bypassed
- Entry Alert: Entry alert in progress
- Fire: Fire alarm active
- Alarm State (Value): 0 – Idle, 1 = Trouble, 2= Alert, 3 = Alarm
- Intruder Alarm- Intruder Alarm Active
- Zone NotReady (value): Zone number which is open in alarm
- Security Off (1-bit): Security Off state On/Off
- Away Mode (1-bit): Away Mode On/Off
- Night Mode (1-Bit): Night Mode On/Off
- Day Mode (1-Bit): Day Mode On/Off
- Vacation Mode (1 bit):Vacation Mode On/Off
|
Posted: Sunday Apr 9th, 2017 02:56 pm |
|
4th Post |
Posted: Friday Apr 28th, 2017 11:14 am |
|
5th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
In Modbus to Comfort, the mapped Comfort registers status can be viewed as well as changed directly - This is a very useful too for testing the Modbus Integration
Check the "Show Status" button to show the actual status of the Comfort Register, eg Flag02 in the example below mapped to Holding Register 400 Hex. Click on the status to change the state of the flag from Off to ON and vice versa. This should change the state of the modbus holding register
In the example below Show Status shows the value of Counter002. Enter a new value in the Status field to change the Counter value. This should afffect the maped modbus register ie Holding Register 400 hex
|