Hi all,

As it says above really. I have a couple of Europa steel enclosures that have switches in them for controlling outdoor lights.

I opened one  of these up yesterday, and noticed an amount of condensation on the inside walls of the cabinet. The cabinets are sealed except where the mounting bolts go through the back. I may unbolt it and fit rubber washers to see if it helps, Is this a common occurence, and if so is there any sensible way of controlling this ?

Cheers,    John.



 Posted: Monday Oct 24th, 2016 08:20 am
   PM  Quote  Reply 
2nd Post
Ingo
UCM Pi Users


Joined: Sunday Jan 21st, 2007
Location: South Africa
Posts: 557
Status: 
Offline

  back to top

I did some research on this a long time ago but never implemented it so can only give you pointers. You need to install a small heater inside the enclosure to keep the temperature just above the dew point. Search on Google for a small heater, similar to a fish tank heater, that you can install inside the enclosure. There is a name for it but I can't remember what it is. Also, don't seal the unit completely. Add a small hole at the bottom of the enclosure.


See below:https://www.automationdirect.com/static/specs/ptcenclosureheaters.pdf

Last edited on Monday Oct 24th, 2016 08:32 am by Ingo



 Posted: Monday Oct 24th, 2016 01:29 pm
   PM  Quote  Reply 
3rd Post
John W
UCM Pi Users
 

Joined: Wednesday Feb 18th, 2009
Location: United Kingdom
Posts: 107
Status: 
Offline

  back to top

Thanks,I didn't realise dedicated heaters existed. After your link i checked and found RS sell these.


I will calculate how big they need to be (your link describes how to do that) and order a couple.


By the way, the cabinet does have a small hole in it, but I sealed it to stop the ants getting in :/



 Posted: Monday Oct 24th, 2016 03:09 pm
   PM  Quote  Reply 
4th Post
Ingo
UCM Pi Users


Joined: Sunday Jan 21st, 2007
Location: South Africa
Posts: 557
Status: 
Offline

  back to top

Put a 'No Ants' sign up but keep it open to equalize pressure and to rid the inside of residual moisture.



 Posted: Monday Oct 24th, 2016 08:51 pm
   PM  Quote  Reply 
5th Post
John W
UCM Pi Users
 

Joined: Wednesday Feb 18th, 2009
Location: United Kingdom
Posts: 107
Status: 
Offline

  back to top

:D

Ordered a pair of heaters from RS, let's hope that addresses it.