I have an integrated comfort / Cbus setup. The cbus has a lux meter installed. Is it possible to get the lux meter to set a comfort flag when ambient light drops below a given value, and then unset it when the light increases above? |
|||||||||
Ingo UCM Pi Users
|
You can try to set your Light Sensor's On/Off setting to a particular Lighting Group address and then set the thresholds for your requirements. Next you will need to map the Cbus Group to a Comfort Flag. I haven't tried it myself but all the components are there so it should work. |
|||||||||
slychiu Administrator
|
agreed it should work make sure you have UCM/Cbus2 to map to flags |