Hi
I have had a ucm for some time and not used or connected it to comfort, however am now extending the system.
Connected ucm to comfort and changed the location to 1 (think 1672) and all LEDs do as they should.
loaded comfigurator (2.10) and tried to upload system imformation - after entering sign-in code a error message comes up "No response from ucm"
Can anyone help please - ucm is 5.43
Regards
David
|
Posted: Thursday Jan 18th, 2007 01:15 am |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
This message is due to the serial port settings on the computer
in Comfigurator, goto Options > Connection and select the COM port which is used to connect the UCM to your computer
There may also be problems with the serial port on the computer
|
Posted: Thursday Jan 18th, 2007 12:05 pm |
|
3rd Post |
llebyat
Member
Joined: | Wednesday Jan 17th, 2007 |
Location: | United Kingdom |
Posts: | 6 |
Status: |
Offline
|
back to top
|
Hi
I did think that it could be to do with the port, so before posting on this fourm for help had tried using a differnt computer and differnt com settings but all i got was an error message " port not found". However on one computer if com1 is selected it asks for sign in code - on my other computer its com8 which then asks for the sign in code.
One computer (com1) has a serial port the other (com8) am using a usb to serial lead and driver (did think it could be that so thats why i tried the other pc with a serial port).
Any other thorghts?
Regards David
|
Posted: Thursday Jan 18th, 2007 12:22 pm |
|
4th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
Check the jumper settings in the UCM Manual
If you dont have this you can download from the website
This may be affecting your UCM
|
Posted: Thursday Jan 18th, 2007 12:35 pm |
|
5th Post |
llebyat
Member
Joined: | Wednesday Jan 17th, 2007 |
Location: | United Kingdom |
Posts: | 6 |
Status: |
Offline
|
back to top
|
Hi
Did check that also before - havent got the ucm with me but recall it being the bottom 3 of a row of i think 7 - all are shorted - is that correct?
|
Posted: Thursday Jan 18th, 2007 12:50 pm |
|
6th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
It is not only the ID settings, there arre other jumpers which have an effect
There is J2, and SW8,
There is also a section on Troubleshooting which gobves some steps on what to check if you hve problems
|
Posted: Thursday Jan 18th, 2007 09:59 pm |
|
7th Post |
llebyat
Member
Joined: | Wednesday Jan 17th, 2007 |
Location: | United Kingdom |
Posts: | 6 |
Status: |
Offline
|
back to top
|
Hi
The j2 jumper is in the rs232 and sw8 f,g,h are all shorted - appears to be correct?
I have another ucm - a old basic one with no only 3 jumpers which are all open and this ucm has no terminals. this ucm acts just the same.
The only thing that i have noticed is that d10 green flashes very slowly and d9 red flashes very very fast which seams to be the opposite to what is stated in your manual?
regards
|
Posted: Thursday Jan 18th, 2007 11:27 pm |
|
8th Post |
adlim
Member
Joined: | Wednesday May 3rd, 2006 |
Location: | Singapore |
Posts: | 210 |
Status: |
Offline
|
back to top
|
If you set it as UCM ID 1, SW7-A, B, C should be shunted.
SW8-F is used for UCM/Ethernet.
SW8-G would disable the STX/ETX.
SW8-H is for flow control.
All these 3 are normally unshunted for UCM01.
So, it seems that you have shorted the wrong jumpers. Please refer to the manual (http://www.cytech.biz/temp/manuals/ucmman.pdf )for more information.
|
Posted: Friday Jan 19th, 2007 12:29 am |
|
9th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
You say you have 2 UCMs which are not able to communicate with the PCs? This indicates that there is a problem wit th PC serial communications
Can you try the PC serial port to another RS232 device if you have one
D10 green led is actually blinking very fast but it pauses occasionally which is the "flash:" that you notice
llebyat wrote: Hi
The j2 jumper is in the rs232 and sw8 f,g,h are all shorted - appears to be correct?
I have another ucm - a old basic one with no only 3 jumpers which are all open and this ucm has no terminals. this ucm acts just the same.
The only thing that i have noticed is that d10 green flashes very slowly and d9 red flashes very very fast which seams to be the opposite to what is stated in your manual?
regards
|
Posted: Sunday Jan 21st, 2007 11:09 pm |
|
10th Post |
adlim
Member
Joined: | Wednesday May 3rd, 2006 |
Location: | Singapore |
Posts: | 210 |
Status: |
Offline
|
back to top
|
When you say all dip settings are set correctly, I gather you mean that SW7 and SW8 are both set correctly? Is SW8-F shorted and SW8-G and SW8-H opened?
If there has been done and you are unable to communicate via Comfigurator, could you post a screenshot of the settings window here so that we can we see what is the cause of the problem? Perhaps you would try to initialise (using the DS Manager) and see if that solves the problem.
|
Posted: Sunday Jan 21st, 2007 11:28 pm |
|
11th Post |
llebyat
Member
Joined: | Wednesday Jan 17th, 2007 |
Location: | United Kingdom |
Posts: | 6 |
Status: |
Offline
|
back to top
|
Hi
Am still having no luck getting a ucm to connect to comfort as per earler posts.
sw7 a,b,c are all shorted
sw8 has no jumpers on at all
j2 is in RS232
loc 1672 is set to 1
ready LED is on
D9/D10 are flashing correct
but following sig-in error message "no response from UCM" appears
ucm is connected to serial port com1
have tested com1 with other devices and all ok
Also
I have cs-xpress software and interface - when connected to com1 and you load the RS485 mointor you can see the tx and rx transmission. However if you download a .csx file it shows the transfer 0-100% and states its completed but following reset nothing has changed.
Am amiss as to what is wrong
all ucm settings appear correct and the comfort side seams ok - so it seams like its a pc problem - yet the port is working and the old cs-xpress software can talk to comfort yet wont over rite even though it states it has.
N.B i have both .csx and .ccl file formats
Any idea's please
David
|
Posted: Sunday Jan 21st, 2007 11:34 pm |
|
12th Post |
adlim
Member
Joined: | Wednesday May 3rd, 2006 |
Location: | Singapore |
Posts: | 210 |
Status: |
Offline
|
back to top
|
Could it be a setting on Comfigurator? Check that the baud rate is set as "9600" and flow control set to "none".
|
Posted: Sunday Jan 21st, 2007 11:41 pm |
|
13th Post |
Posted: Monday Jan 22nd, 2007 12:35 am |
|
14th Post |
adlim
Member
Joined: | Wednesday May 3rd, 2006 |
Location: | Singapore |
Posts: | 210 |
Status: |
Offline
|
back to top
|
llebyat wrote: both those settings are correct?
What is your Comfort firmware version?
|
Posted: Monday Jan 22nd, 2007 12:18 pm |
|
15th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5493 |
Status: |
Offline
|
back to top
|
Adrian has replied to your post and is waiting for the result
In future I suggest you start a new topic instead of replying to a post by someone else as it causes confusion as you can see from this topic
regards
---UCM Ethernet Topic Moved---