I am having Daikin aircon indoor units which can not be detected for Run/Stop status with CSM03-PCB.

The reason is standby/ run currents of these indoor units are unfortunately not much differrent and also so small between states: OFF state with 40-50mA (Standby current) and RUN state with only 90-100mA.

So far I have adjusted sensitive jumpers, tried to open-short 2-pins of indication LED, double power wires going through hole of CT.... and still can not detect the right OFF-RUN states of these units via CSM03-PCB (which its highest sensitivity is OFF with <50mA and RUN with >100mA)?

Any one faced same problem and how to sove it? I connect these CSM03-PCB via RIO' input.

Thanks

 



 Posted: Monday Apr 13th, 2015 01:09 pm
   PM  Quote  Reply 
2nd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

You are usiing the old CSM03-PCB with indicator LEDs
Can you use the the new ones without led

Is the CSM03 always detecting curent  when aircon off or is it not able to detect on when the aircon is on?
How did you measure the standby and on  current? 40 and 90 ma seems to be to litlle
difference

If you reduvce the temperature setting, is the curent sensor able to detect?



 Posted: Monday Apr 13th, 2015 01:21 pm
   PM  Quote  Reply 
3rd Post
namnp
Comfort Distributors
 

Joined: Monday Jul 31st, 2006
Location: Vietnam
Posts: 35
Status: 
Offline

  back to top

Yes, it may be the old version PCB with Led indicators. It worked well to detect indoor units always "OFF" (even it actually running with current as was measured by Clamp Current meters, as low as 90-100mA). Or if doing twice wirings through hole of CT, it detect always "ON", because of standby current even unit actually being Off!
If the new version CSM03-PCB (without indicator Led) can solve this?



 Posted: Monday Apr 13th, 2015 01:23 pm
   PM  Quote  Reply 
4th Post
namnp
Comfort Distributors
 

Joined: Monday Jul 31st, 2006
Location: Vietnam
Posts: 35
Status: 
Offline

  back to top

What is temperature setting ? In which part of comfigurator?



 Posted: Monday Apr 13th, 2015 01:40 pm
   PM  Quote  Reply 
5th Post
namnp
Comfort Distributors
 

Joined: Monday Jul 31st, 2006
Location: Vietnam
Posts: 35
Status: 
Offline

  back to top

Uhm, do you mean Fan Med or Fan High speeds instead of Fan Low speed?
These indoor aircon units are indoor parts of Daikin VRV III system.
Will try tomorrow with lower tenperature setting!



 Posted: Monday Apr 13th, 2015 02:07 pm
   PM  Quote  Reply 
6th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

Try lower temp and higher fan speed
we dont have the old csm with leds so we do not know if they have other problems
These were produced a long time ago, so it iss better to try new ones

if the difference between standby and oon is only 40 ma this may not work well




 Posted: Tuesday Apr 14th, 2015 10:26 am
   PM  Quote  Reply 
7th Post
namnp
Comfort Distributors
 

Joined: Monday Jul 31st, 2006
Location: Vietnam
Posts: 35
Status: 
Offline

  back to top

I haved tried with High Fan 24 degree On/Off: it work well!. Other cases, It did not work well for detecting state.

Therefore, It may need a more sensitive either "CT-new" or "CSM04-PCB" to install with newly energy saving equipment.
So far, it can not work to detect state with old CT and old CSM-PCB for normal operation (Fan medium, 25 degree...). Do hope there would be new devices/ solution for such cases in furture.



 Posted: Tuesday Apr 14th, 2015 12:57 pm
   PM  Quote  Reply 
8th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

yes we are working on new devices which will be able to tell the difference



 Posted: Tuesday Apr 14th, 2015 04:53 pm
   PM  Quote  Reply 
9th Post
juwi_uk
Member


Joined: Friday May 25th, 2007
Location: Newbury, United Kingdom
Posts: 1255
Status: 
Offline

  back to top

Any chance of ones that clip around the wire like you see on aftermarket units (my CurrentCost sensors are like this) rather than have to pass the wire through the hole (i.e. have to disconnect stuff) to fit it?

Just a thought and IMHO.

J

 

 

 

 



 Posted: Wednesday Apr 15th, 2015 06:44 am
   PM  Quote  Reply 
10th Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5493
Status: 
Offline

  back to top

The sensitivity of the clip on sensors is not hgh as they are used for larger loads