I need to send a phone call ( with specific words ) when a input on RIO became active
I have rainwater reservoir with two pumps and 4 level buoys, one for stop, one for start first pump, one for second pump ( and high level alarm ) and the last for critical level.
Any time i reach high level alarm i need to send a phone call and when i reach critical level i also need to send a phone call .
Thus anyboby know how to do this.
|
Posted: Sunday Apr 12th, 2015 06:46 am |
|
2nd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
The RIO inputs cannot be used for alarm
The Comfort and SLave inputs can be used to trigger alarms
Only alarms can cause a dial out. When the alarm dials to a Voice Phone, it will announce the alarm Type and the zone
Input -> Zone Type -> Alarm Type -> Dial out to 8 phones -> announce alarm Type and Zone Name
Hence you shuld colnnect these inputs to input of Comfort, LEM or SEM
|
Posted: Sunday Apr 12th, 2015 01:53 pm |
|
3rd Post |
batman
Member
back to top
|
CAn't use virtual input to do this? because i don´t have cables to reach my confort
|
Posted: Monday Apr 13th, 2015 06:27 am |
|
4th Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5500 |
Status: |
Offline
|
back to top
|
Virtual Inputs can be assigned by some external UCMs like Cbus, KNX, Zwave etc
RIOs are designed for non-alarm applications
You can add a Slave SEM02 at the same location and use the Slave Inputs instead of RIO
|
|