Hi
I did the physical association in Vera connecting to the outside lights and that worked fine.
I have the PIR next to me with no back on and as you suggest I just pick it up off the table which triggers the wake up process.
I will try group one over the weekend, do you think I need to fill in Vera info as well as HS?
I think the association has worked in HS, however, this all depends on if the status change on node 25 my cytech virtual node is dependant on a response back from the virtual node (VN). I can see the status change on the PIR but the VN remains off.
I can trigger the VN manually in both Vera and HS and I get a status change on both interfaces. I have setup the VN in comfort as a virtual input but whatever I use as the on or off response doesn't work.
Thanks for all your help, I am sure it will work at some point just a matter of getting the right process sorted.
Cheers
Lee
|
Posted: Friday Oct 10th, 2014 10:37 am |
|
22nd Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
sorry should have asked what info describes the VN. In both HS and Vera it has been setup as a dimmer switch.
|
Posted: Friday Oct 10th, 2014 11:34 am |
|
23rd Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
"In both HS and Vera it has been setup as a dimmer switch."
In my opinion, dimmer switch is good enough, as long as the VN responds correctly.
"I have setup the VN in comfort as a virtual input but whatever I use as the on or off response doesn't work."
Other than writing to UCM/Zwave EEPROM, make sure you write to Comfort (Zones/Inputs) as well.
You can monitor the zone status in Comfigurator. Under Zones/Inputs, select the zone and check "Show Status"(Zone Properties on the right). The "Zone State" will display the current state.
|
Posted: Wednesday Oct 15th, 2014 12:13 am |
|
24th Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
Hi,
I have not got much further with this, however, I would just like to confirm that when I change state of the VN using either HS or Vera they show a graphical status change (on or off)
Unfortunately if I monitor the virtual input it remains inactive at all times.
In normal association processes you would normally would put the controller in to association mode and the hit the send button in comfigurator to confirm the association. However, the way HS and Vera do this it seems to all be done in software without the need to press buttons.
Cheers
Lee
|
Posted: Wednesday Oct 15th, 2014 12:15 am |
|
25th Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
Oh I have tried group one and no difference.
Do you have Vera in the cytech lab if so have you managed to to an association?
|
Posted: Wednesday Oct 15th, 2014 04:48 am |
|
26th Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
lwillerton wrote: In normal association processes you would normally would put the controller in to association mode and the hit the send button in comfigurator to confirm the association. However, the way HS and Vera do this it seems to all be done in software without the need to press buttons.
Actually, association is to program association setting in the source (triggering) node only and not on the target nodes.
For (remote) controller operation, the send button is to indicate which node to be added in association mode, before programming the source node.
As users can select the nodes in HS and Vera already, hence the send button to indicate which node is not necessary anymore. Last edited on Wednesday Oct 15th, 2014 04:49 am by leonchue
|
Posted: Wednesday Oct 15th, 2014 05:01 am |
|
27th Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
lwillerton wrote: Oh I have tried group one and no difference.
Do you have Vera in the cytech lab if so have you managed to to an association?
We managed to source a Vera Lite to test it out. We have no problem in getting virtual node to work after association.
However, we confirmed that the manufacturer query for virtual node has a bug and will patch that in the next release.
My guess is that SP103 is not associated properly. Did you trigger its tamper switch to keep the RF(Z-Wave) awake for 10 mins when doing association? The RF side may be switched off when you do the association process.
|
Posted: Wednesday Oct 15th, 2014 05:01 am |
|
28th Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
Ok I am just sitting with the setup now and I am please to see that I am doing things right.
So what I have found out tonight is if I setup the association in Vera (main controller) and click update on HS on the PIR node it pulls the association information through.
Both HS and Vera show a status change of the PIR in sync the only thing is the status of the comfort VN doesn't change in any of the systems.
If I go in to comfort Under Zones/Inputs, select the zone and check "Show Status"(Zone Properties on the right). The "Zone State" will display the current state. and tick and untick the box it always remains inactive
I am confident that the association is working in principle its just not updating comfort. By all accounts I should not need to write to the eprom after and new association is created, but I have tried this on several occasions.Last edited on Wednesday Oct 15th, 2014 05:03 am by lwillerton
|
Posted: Wednesday Oct 15th, 2014 05:08 am |
|
29th Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
If you click virtual node on/off in Vera or HS, does the zone state change?
|
Posted: Wednesday Oct 15th, 2014 05:13 am |
|
30th Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
yes but not in comfort
|
Posted: Wednesday Oct 15th, 2014 05:18 am |
|
31st Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
Just done a learn from vera in to comfort and uploaded to eprom, no change
|
Posted: Wednesday Oct 15th, 2014 05:19 am |
|
32nd Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
For trouble-shooting, change the virtual node mapping to a counter. Write EEPROM. Read EEPROM to confirm changes.
Then trigger VN via Vera/HS again. See if that counter changes state.Last edited on Wednesday Oct 15th, 2014 05:20 am by leonchue
|
Posted: Wednesday Oct 15th, 2014 05:32 am |
|
33rd Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
Nice one...that works I can see the value change from 0 to 255 when the PIR is triggered.
|
Posted: Wednesday Oct 15th, 2014 05:40 am |
|
34th Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
That is great! We are so close now.
Now revert VN mapping back to Virtual Input. Remember to write UCM/Zwave and Comfort.
|
Posted: Wednesday Oct 15th, 2014 06:00 am |
|
35th Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
OK done that and back to no status change...I have assigned to input 18 and checked.
|
Posted: Wednesday Oct 15th, 2014 07:09 am |
|
36th Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
lwillerton wrote: OK done that and back to no status change...I have assigned to input 18 and checked.
Did you program zone type for 18 as well? If it is blank, the zone is ignored and status is not updated.
Otherwise, zone 18 operates as what it is, be it security or automation.
|
Posted: Wednesday Oct 15th, 2014 10:46 am |
|
37th Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
Hi,
It looks like I have removed this setting so will give it a go tonight. Will Zone type Monitor N/C or N/O do?
Cheers
Lee
|
Posted: Wednesday Oct 15th, 2014 11:17 am |
|
38th Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
lwillerton wrote: Hi,
It looks like I have removed this setting so will give it a go tonight. Will Zone type Monitor N/C or N/O do?
Cheers
Lee
It depends on what you want to achieve.
Monitor N/C or N/0 triggers FamilyCare alarm in all security modes (by default). So I am not sure if that is really what you want.
Maybe you can test with "SwitchNO" or "SwitchNC" first.
Last edited on Wednesday Oct 15th, 2014 11:23 am by leonchue
|
Posted: Wednesday Oct 15th, 2014 09:46 pm |
|
39th Post |
lwillerton
Member
Joined: | Sunday Oct 2nd, 2011 |
Location: | |
Posts: | 221 |
Status: |
Offline
|
back to top
|
It's worked thank you so much...so what do you think caused the problem?
|
Posted: Thursday Oct 16th, 2014 05:08 am |
|
40th Post |
leonchue
Cytech
Joined: | Monday Aug 7th, 2006 |
Location: | Singapore |
Posts: | 71 |
Status: |
Offline
|
back to top
|
lwillerton wrote: It's worked thank you so much...so what do you think caused the problem?
That's great.
The problem? Initially, it was the unsuccessful association with VeraLite. After that, the virtual input was not validated in Comfort (without setting zone type).
|