webloader Member
|
I want to be able to log zone activations, but without changing their zone types. The reason for this is that I have a Neato (Roomba like robot vacuum) that is setting off the alarm when the house is in away mode. I want to be able to let it run through multiple clean cycles, during multiple days and examine which sensors need to be replaced. Is there a way Comfigurator can be left running in the monitor mode without it timing out? Also in the monitor window it would be really useful if it timestamped everything.. |
|||||||||
Ingo UCM Pi Users
|
Try ComfortClient, it logs all activities to a daily log file. It's also comma separated so you can import into Excel and do some neat stuff there. Ingo |
|||||||||
ident Administrator
|
the UCM/USB will not log out by time UCM/ETH0x will log out after 2 minutes by default but that can be changed in the DS Manager or Comfort server manager to value of eisded 0 to never log out You can also use Bus Monitor in Tools which has a time stamp, but this may end up with a lot of info because that logs all the cmmunications on the bus |