Hi

My system has two magnetic contacts which are labelled as 4k7. They measure 4k7 on open and about 9k2 on close of the magnetic contact.

Comfort input is configured as double EOL.

Comfort always sees this input as "on", regardless of open or closed door/window. Opening or closing the door/window however does always trigger a "zone on" event.

How can I get this input to be correctly seen as open or closed?

Steef

Last edited on Monday Dec 16th, 2013 04:50 pm by steefdebruijn



 Posted: Tuesday Dec 17th, 2013 12:23 am
   PM  Quote  Reply 
2nd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

Comfort double EOL requires aa 2k2 resistor in series and 4k7 in parallel


Do you mean that the magnetic contact has built-in EOL resistors? Thhat means that the contact was designed for some other system which can accept these values. You need to be able to remove the 4K 7 series resistor and use the 2K2 series resistor provided with Comfort. Or get  another magnetic contact



 Posted: Tuesday Dec 17th, 2013 04:27 am
   PM  Quote  Reply 
3rd Post
steefdebruijn
Member
 

Joined: Sunday Jul 29th, 2012
Location: Netherlands
Posts: 28
Status: 
Offline

  back to top

Yep build in resistor.

Bummer.

Thanx!