Comfort Automation/ Security System Forums > Support > Comfort as Fire Alarm > Wiring multiple ESP Fireline detectors to a single zone

Wiring multiple ESP Fireline detectors to a single zone
 Moderated by: slychiu, Home
 New Topic   Reply   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Thursday Nov 14th, 2013 08:53 pm
   PM  Quote  Reply 
1st Post
Orinoco
Member
 

Joined: Thursday Nov 14th, 2013
Location:  
Posts: 2
Status: 
Offline

  back to top

I'm trying to wire 3 ESP Fireline smoke/heat detectors into my Comfort system and I'm having a little trouble deciding where to put the resistors. I've looked at the wiring diagram for four wire smoke detectors in the quick installation guide and I believe I can follow it to connect each detector into a separate zone, but I don't have enough spare zones to allow that - I need all three connected together into a single zone.

I have the optional relay bases for the detectors so I can use the wiring diagram from this 2 page pdf:

ESP PSD212 manual

I just need to know where to put the 4k7 resistor (or resistors if more than one is needed). Any suggestions?



 Posted: Friday Nov 15th, 2013 01:28 am
   PM  Quote  Reply 
2nd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

In the attached figure 4, use 2K2 resistor in place of the 1K resistor shown for the series EOL resistor

The 4K7 parallel resistor is more tricky. It has to be in parallel to all the contacts
It should be connected between the NC terminal of the last detector (conected to the series resistor) and the COM terminal of the 1st detector (connected to ZONE).





 Posted: Friday Nov 15th, 2013 10:24 am
   PM  Quote  Reply 
3rd Post
Orinoco
Member
 

Joined: Thursday Nov 14th, 2013
Location:  
Posts: 2
Status: 
Offline

  back to top

Thanks for your help, I'll give it a go.



 Posted: Friday Nov 15th, 2013 03:52 pm
   PM  Quote  Reply 
4th Post
juwi_uk
Member


Joined: Friday May 25th, 2007
Location: Newbury, United Kingdom
Posts: 1255
Status: 
Offline

  back to top

Probably a silly question but why bother with EOL at all for alarm zones as surely tamper is less important for these types of zone?

Julian



 Posted: Saturday Nov 16th, 2013 01:00 am
   PM  Quote  Reply 
5th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

It tells you when the wire is broken and gives a zone trouble rather than a fire alarm which may cause everyone to run out of the house