I have a pair of KP05 keypads connected to Comfort II Ultra with 7.032 firmware; Keypads are 1.19.

In 'Security Off' mode, the text name of each zone is displayed on the LCD whenever they are triggered. Each zone/input has 'Show Status' set at No.

Is there anyway to stop the keypads displaying this except when in Alarm state etc?

Thank you!

Simon

ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

The show status in Zones for Comfigurator shows the actual zone status in Comfigurator, and does not affect the zone display on  the keypads

You cannot stop the zones from being displayed on the keypads unless they are not displayed in alarm as well

There is another option in Modules and Settings "Show alarms" checkbox. If unchecked the keypads will not display any alarm information at all unless you sign in, and only for 30 seconds, This is for EN50131 but I do not recommend that as it hides information from you

May I ask why you want the zones not to be shown in security off? Does it cause any problem?


simond
Member
 

Joined: Saturday Jan 24th, 2009
Location: United Kingdom
Posts: 35
Status: 
Offline

  back to top

Its not a big problem - its just I had a lot of detectors both inside and out in a busy house, and the keypad is always showing different text... rather than 'Security off'. I was just being picky really :-).
Thanks for the help.