How do you set a Zone Type to 0? If I set it to 'Blank' then it saves the value as 'nothing'. Documentation says it needs to be '0' for Analog Input measurement.
Below is an example of type 'Blank' en type 0
<Zone Number="4" Name="Zone4" ZoneTypeName="" EntryPath="false" Restore="false" Partition="0" Eol="EolShunts" VirtualInput="false" Announce="false" />
<Zone Number="5" Name="Zone5" ZoneTypeName=" " EntryPath="false" Restore="false" Partition="0" Eol="EolShunts" VirtualInput="false" Announce="false" />
Thanks,
Ingo
|
Posted: Thursday Feb 7th, 2013 01:53 am |
|
2nd Post |
ident
Administrator
Joined: | Wednesday Aug 9th, 2006 |
Location: | Singapore |
Posts: | 3493 |
Status: |
Offline
|
back to top
|
Setting to blank is zone type 0
What you have shown for zones 4 and 5 are zone type 0
|
Posted: Thursday Feb 7th, 2013 02:21 am |
|
3rd Post |
Ingo
UCM Pi Users
Joined: | Sunday Jan 21st, 2007 |
Location: | South Africa |
Posts: | 557 |
Status: |
Offline
|
back to top
|
The " " must be from previous versions of Comfigurator then as zones 65 to 96 shows "".
Thanks.
|
|