Hi,

I just upgraded to the new Comfort Gen II board.

The main reason for the upgrade was to use 4 Rios and 8 Scence switches.

I am using the new Configurator V2.1.0.

When I try to increase the Number of SCS/RIO, it would not allowed more than 8 (range 0 to 8).

Please let this be a Configurator issue and NOT an issue with the new board.

What would be a work around as I set this weekend to complete my installation.

PLease help

 

REUBEN

South Africa

 

 

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

It is a problem with Comfigurator which limits the number to 8
Use your keypad to set the number of SCS/RIO in Location 1676, then reset
The next version will have this fixed

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi,

What would happen when I do a download, would it reset it back to 8 ?

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

yes, it would

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Thanks,

When can we expect a software fix ?

ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

The next version 2.2.0 of Comfigurator is a major upgrade and is many months away
In the meantime I think this workaround can handle the situation as you would not need to download so often
regards

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

I still have problems

1. Setting location 1676 to 9 and using ANY of the 7 available addresses( I used 8 already) gives me a communication failure 89.

2. The SCS/RIO in Comfigurator only handles 64 responses  129 -193 (129 + (8 X 8)).

This is major set back for me as this is my third upgrade to just accomodate my installation of 12 RIOS/SCS.

Months away from the next release  is disappointing.

What's my alternatives/work around (if any, at this stage) ?

Thanks

 

 

ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

Have you set the ID switches for J1 (A to D) for ID 9 accordiing to the RIO Manual?
You should not be seeing Commmunications Failure 89 if it is correct
You should also reset Comfort after changing the location 1676
There are locations for programming RIO responses oncxe you have fixed the communications problem

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

The chances of me not setting the jumper settings incorrectly is pretty much slim at this stage considering I have 8 such address already working.


I did reset the system after setting location 1676 to 9.


It is a Scene switch that is giving me this problem not a RIO. Would you get a communication error if there are no responses associated with an address ?

May I be bold in asking whether the Comfort GEN II has been tested for more than 8 RIO/SCS ?

If yes, what could the problem be other than an incorrect address ?

Thanks

Reuben

 

 

Last edited on Saturday Sep 9th, 2006 11:44 am by dcrera

adlim
Member


Joined: Wednesday May 3rd, 2006
Location: Singapore
Posts: 210
Status: 
Offline

  back to top

Hi Reuben,

When you said "Setting location 1676 to 9 and using ANY of the 7 available addresses( I used 8 already) gives me a communication failure 89", do you mean to say that you tried to change the ID jumpers without resetting the SCS/RIO after doing so?? The SCS/RIO would need a power cycle as well after you change the jumpers.

To program the responses, you could make use of keypad programming at this stage.

Regards.

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi,

When you said "Setting location 1676 to 9 and using ANY of the 7 available addresses( I used 8 already) gives me a communication failure 89", do you mean to say that you tried to change the ID jumpers without resetting the SCS/RIO after doing so?? The SCS/RIO would need a power cycle as well after you change the jumpers.

Yes I did a reset

Would the SCS led's flash if no reponse is associated with a switch ?

Where can I find the doco to load SCS/RIO reponses via the keypad ?

Is there a .bat file I can use to upload these using RS232 comms ?

 

adlim
Member


Joined: Wednesday May 3rd, 2006
Location: Singapore
Posts: 210
Status: 
Offline

  back to top

Yes, the SCS LED will flash if no response is assigned to the buttons and the button is pressed as mentioned in the SCS manual under "LED indicator".

Guess you would need to read up the "Action Codes Reference" and "Engineer Menu Programming" to get an idea of how to program using the keypad.

There is no executable file for the response assignment at the moment.

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi,

This is a slog. You know what I need to do, can you assist me by giving me the reference  page numbers of the "Action Codes Reference" and "Engineer Menu Programming" manual to fast track this process.

 

Thanks

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

You will have to solve the problem as to why the RIO is not being detected. Comms failure 89 means that Comfort is not seeing the RIO on ID 9. That is regardless of whther Comfort II works with 15 RIOs or not (which it does).  As Adrian says, power off and on the RIO after setting the ID
The updated RIO  manual showing the Locations for programming RIO responses is now on the website in the Manuals  section. This gives you the locations to proram the responses using the keypad in Engineer Menu 7,4,1 (Locations Menu)


Last edited on Monday Sep 11th, 2006 01:32 pm by slychiu

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi,

Thanks, will play around with this during the week and will feedback with my progress.

I noticed that the location numbers are different for RIO 1- 8 in file system 24 compared to file 34.

So guess that my current 8 RIO/SCS would have new locations after converting from 24 to 34 file system.

 

Last edited on Monday Sep 11th, 2006 02:04 pm by dcrera

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

No, the RIO locations for File System 24 and 34 are identical
Locations for File System 18 are different from that of 24 and 34
Please note that for File system 24 and 34, each Response requires 2 locations as explained in that section aboujt the locations

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

You are quite right, yet again. :P

Seems like I missed a system reset somewhere for comms failure 89, so that fine.

Implementing RIO 9, I go the location menu and select 4736 and I am prompted for a code. I assumed this code to be a response number, so I entered 181 for 4736 and 4738.

I then went to the programming response menu

Entered response no 181#

then

128,181,2,128,193,2,255

I did  a system reset

Undid and replaced the power on the SCS 

Pressed button 1 and it flashes non stop.

My intention was to toggle the state of output 181 (from RIO7) and 193 (RIO9)

What am I missing ?

 

NB : On RIO 7, I have the following outputs still available 181 to 184 (unused)

 

Last edited on Monday Sep 11th, 2006 05:34 pm by dcrera

adlim
Member


Joined: Wednesday May 3rd, 2006
Location: Singapore
Posts: 210
Status: 
Offline

  back to top

Hi,

I suspect that you might have left out programming locations 4737 and 4739. Guess you might have missed out on this point in the worksheet:

"Response Numbers have to be entered in 2 successive Locations. If the Response number is less than 256, enter the Response number in the 1st location and enter 0 in the next location. For example to enter Response 123 for SCS/RIO ID 1, Input 2 - ON Response, enter 123 in Location 4484 and 0 in Location 4485. If the Response number is greater than 255, divide the number by 256, and enter the remainder in the first location and the quotient in the 2nd location. For example, to enter Response 1000 in SCS/RIO ID 1, Input 2 - ON Response, 1000/256 = 3+ 232/256. Enter 232 in Location 4484 and 3 into Location 4485"


What you have programmed are actually the ON/OFF responses instead.


Hope this helps.

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi,

You can't possibly be serious !!

This is becoming quite tedious, how long did you say before  the next release of Comfigurator ?

As an interim solution, take my example of the outputs I want to toggle, is it possible for you to put this formula/calculation on a spreadsheet and indicate with columns would be used in the location codes ?

A detailed flow of my example would be a nice place to start.

Your co-operation will be highly appreciated

 

 

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

If you response numbers are less than 256 then it is simple, just set the next location to 0
-----------------------------------------------------------------------------------------------------
Implementing RIO 9, I go the location menu and select 4736 and I am prompted for a code. I assumed this code to be a response number, so I entered 181 for 4736 and 4738.

I then went to the programming response menu

Entered response no 181#

then

128,181,2,128,193,2,255
-----------------------------------------------------------------------------------------------
In your example above, you just need to set Location 4737 and 4739 to 0

I dont think it is that challenging

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Fine, I will give it a try and will feedback tonight on my progress.

Just for my clarity, if my response no was, let say 196, then 196 would be entered in location 4736 and 4738 , 0 in location 4737 and 4739.

And this string 128,181,2,128,193,2,255


would read like this :

Toggle output 181 (Rio output)

Toggle output 193 (Scs Led output)

I just want to clear up any confusion with Reponse 181 and output 181 from my previous example.

Thanks

 

 

 

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

dcrera wrote: Fine, I will give it a try and will feedback tonight on my progress.

Just for my clarity, if my response no was, let say 196, then 196 would be entered in location 4736 and 4738 , 0 in location 4737 and 4739.

And this string 128,181,2,128,193,2,255

would read like this :

Toggle output 181 (Rio output)

Toggle output 193 (Scs Led output)

I just want to clear up any confusion with Reponse 181 and output 181 from my previous example.

Thanks



That is correct

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Thanks a stack

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

YES, it's working.

 

Thanks again

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

I am sure you had no doubts that it would work  ;)

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Sure, it's just cumbersome work.

Thanks for all your assistance.

 

 

 

Last edited on Wednesday Sep 13th, 2006 10:38 am by dcrera

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

I am a sucker for punishment; any day of the week.

Well, I thought that having an LCD keypad (KP04) would help with programming via the keypad (I changed from KP02), just to see that I am keying in the right info.

It turns out that my UCM is version 5.43 and not 5.72 so syncing is not possible.

Seems I need another upgrade for my UCM.

When I download to update the vocab, would it undo all my work I did on setting up  location 1676, and my new responses ?

Thanks

 

 

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

For Vocab Download you need UCM 5.92 firmware
This version allows you to sync with the KP04 by pressing two keys.
It will allso do a normal download much faster than an older version
As yoiur version 5.43 was released many years ago, it is not able to support these new requirements for the KP04 and Comfort II.

adlim
Member


Joined: Wednesday May 3rd, 2006
Location: Singapore
Posts: 210
Status: 
Offline

  back to top

However, please note that the pressing of two buttons (* and 1) to sync would require KP04 of version 1.03 and above.

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Fine,

When I do get to do the download, would it effect any changes I am making via the Eng Menu ?

Thanks

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

dcrera wrote: Fine,

When I do get to do the download, would it effect any changes I am making via the Eng Menu ?

Thanks

A Vocab download would not affect the programming at all
A normal program download would change the Numb ber of RIO/SCS. However it should not affect the locations that you are programming for RIO 9 to 15 Responses as these are not within the programmed range of RIO 1 to 8
To play safe do a Selectve download, uncheck Modules and settings  and RIO/SCS responses

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Thanks

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Last edited on Tuesday Oct 17th, 2006 01:52 pm by dcrera

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi Chiu,

I decided that I will wait for a new release of Comfigurator. Any idea when we could expect one that will handle 15 SCS/RIO's ?

Thanks

 

 

ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

We expect that to be available in November

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

That's great.

Thank You

 

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi Chiu,

Do you have a release date in November ? Is there a beta version to handle 15 RIO/SCS for the interim?

Thanks

 

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

I cannot promise an availability date yet, but it will be released as beta first. The 15 RIOs will definately be included

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi,

I have some time off during the Christmas period. Any possibilities for a beta release  before Christmas ?

Thanks

 

 

Last edited on Wednesday Nov 22nd, 2006 12:38 pm by dcrera

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

We expect beta release in November so you have plenty of time before Xmas

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Sorry, make that early December

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Thanks, I will be on the look out

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Comfigurator 2.1.2 (beta) is available with 15 SCS/RIO, see http://www.comfortforums.com/forum20/369.html

dcrera
Comfort Installers


Joined: Monday Aug 7th, 2006
Location: Durban, South Africa
Posts: 279
Status: 
Offline

  back to top

Hi Guys,

A big thank you for this release. My HA project is finally done.

I had no issues with this release, all worked just fine for me.

Thanks

 

 

 

slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

Great. I hope you have many more projects like that