Posted: Monday Sep 28th, 2009 02:12 pm |
|
21st Post |
ident
Administrator

Joined: | Wednesday Aug 9th, 2006 |
Location: | Singapore |
Posts: | 3494 |
Status: |
Offline
|
back to top
|
we will sort out one tomorrow
|
Posted: Tuesday Sep 29th, 2009 08:38 am |
|
22nd Post |
ident
Administrator

Joined: | Wednesday Aug 9th, 2006 |
Location: | Singapore |
Posts: | 3494 |
Status: |
Offline
|
back to top
|
Bernard
We tested 1 FPR here nad found that one of the fingerprint readers had a problem - that the TD+ and RD- on the controller unit was swopped around on the FPR Controller unit. The D11 Green LED on the UCM/Access was permanently on when the JP1 KA/KB is connected, and the led goes off when the terminal block is disconnected
When the KA/KB on JP1 is reversed by plugging the terminal block in the reverse direction then the communications between the UCM and FPR started to work.
Another FPR that we have here did not have this problem and the TD and RD terminals are correct
Can you check if this is the case with your FPR on your bench? The D11 Green LED would be permanent on in this case
We will send one correct FPR and UCM to you with the wires intact as we used to test.
|
Posted: Tuesday Sep 29th, 2009 08:44 am |
|
23rd Post |
technik23
Member
Joined: | Tuesday Mar 18th, 2008 |
Location: | |
Posts: | 36 |
Status: |
Offline
|
back to top
|
Glad it wasn't me. Reversing the KA/KB works! I'll test it on another installation this afternoon. Don't bother sending another unit until I test all our units.
Thanks
P.S. Any thoughts on identifying the use in teh log files thread?
|
Posted: Tuesday Sep 29th, 2009 12:20 pm |
|
24th Post |
ident
Administrator

Joined: | Wednesday Aug 9th, 2006 |
Location: | Singapore |
Posts: | 3494 |
Status: |
Offline
|
back to top
|
We will let you try a test firmware soon which allows this
|
Posted: Friday Oct 2nd, 2009 03:20 am |
|
25th Post |
slychiu
Administrator

Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5085 |
Status: |
Offline
|
back to top
|
We have found the problem with the Autostar units
There is a DIP switch next to the TD/RD connectors which sets Rs232 or RS485 interface
For RS485 1,2,3 should be ON and 4,5,6,7,8 should be OFF. There is small marking on the DIP switch indicating this
Hence for the units which you have to reverse the connections, they are actually set to RS232. This may work but there is distance limitation which may have an effect, so you should change the switch settings to RS485 and reverse your KA/KB connections to the original
This was not known to us before. We will amend the documentation accordingly
|
Current time is 07:03 pm | Page: 1 2 |
|