Lightning Strike causing Problems
 Moderated by: admin
 New Topic   Reply   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Thursday Jun 18th, 2009 10:29 am
   PM  Quote  Reply 
1st Post
Warby
Member
 

Joined: Thursday Aug 2nd, 2007
Location: United Kingdom
Posts: 101
Status: 
Offline

  back to top

Hi,

On a job where the house has been it by a lightning strike. Since then there has been a low battry warning from slave2 and a comms failure from D/S 02

THe battry seems to be trigging the low battry alarm then restoring straight away. There is nothing wrong with the battry.

06/18 09:54 Low Battery # Slave 2
06/18 09:54 Alarm Type # LowBattery (7)
06/18 09:54 Low Batt Restore # Slave 2
06/18 09:54 Low Battery # Slave 2
06/18 09:54 Alarm Type # LowBattery (7)
06/18 09:54 Low Batt Restore # Slave 2
06/18 09:54 Dial Number # 1
06/18 09:54 Low Battery # Slave 2
06/18 09:54 Alarm Type # LowBattery (7)
06/18 09:54 Low Batt Restore # Slave 2
06/18 09:54 Low Battery # Slave 2
06/18 09:54 Alarm Type # LowBattery (7)
06/18 09:54 Low Batt Restore # Slave 2

the DMo2 is also connected to slave 2 and seems to be working fine now i have reset the system.
System has been in for six monthes with no problems.
UltraII 5.145 Slave 2 is 5.100
3 slaves, 2x DM02.

Any ideas where the fault could be?



 Posted: Thursday Jun 18th, 2009 11:16 am
   PM  Quote  Reply 
2nd Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

It looks like something in the Slave was damaged by the lightning. It seems to be not detecting the battery voltage correctly
Can you confirm by replacing the slave?
Or since you have 2 slaves swop the addresses gto confirm if it is Slave #2



 Posted: Thursday Jun 18th, 2009 12:11 pm
   PM  Quote  Reply 
3rd Post
Warby
Member
 

Joined: Thursday Aug 2nd, 2007
Location: United Kingdom
Posts: 101
Status: 
Offline

  back to top

I have swapped slave 2 with slave 3 but there is no faults at the moment so we will moniter.

Also the log shows it was dialling out for engineer sign in(30). the alarm type was set not to dial out (default) I have downlaoded the config and it doesn't seem to be now.



 Posted: Thursday Jun 18th, 2009 12:18 pm
   PM  Quote  Reply 
4th Post
ident
Administrator


Joined: Wednesday Aug 9th, 2006
Location: Singapore
Posts: 3493
Status: 
Offline

  back to top

The lighting strike must have given your Comfort temporary insanity, but it still survived which shows how sturdy it is