 Moderated by: slychiu
 New Topic   Reply   Printer Friendly 
 Rate Topic 
AuthorPost
 Posted: Saturday Dec 6th, 2008 04:42 pm
   PM  Quote  Reply 
1st Post
palmlodge
Member
 

Joined: Thursday Dec 14th, 2006
Location: United Kingdom
Posts: 507
Status: 
Offline

  back to top

I've noticed this a few times - estimating once out of every 5 times

I have a response which is supposed to send an ON command to zwave id#4, and mostly it works - but occaisionally it doesnt - it actually sends an OFF command to zwave id#3

This is shown by the counters (logged in homeseer also) and the zw#3 being turned off. when zw3 is turned off, zw4 is not turned on when it should be.

If i tell the same response to action again, it then works for a few times more.

tia


Im summary
CBUS DLT button press tell Comfort to turn on the plasma via RS232, turns on the amp via CBUS relay, tell the amp to switch IR, and send ZW4-ON to enable the HDMI matrix. ZW3 is not referenced anywhere near these responses (ZW3 is an office printer).



Last edited on Saturday Dec 6th, 2008 04:46 pm by palmlodge



 Posted: Sunday Dec 7th, 2008 05:24 pm
   PM  Quote  Reply 
2nd Post
palmlodge
Member
 

Joined: Thursday Dec 14th, 2006
Location: United Kingdom
Posts: 507
Status: 
Offline

  back to top

Here's another example - different result this time.

TVPower is the CBUS Button - 255 for on, 0 for off. These are all triggered by this button.
As part of the response, when this cbus button is set to ON, ZWave ID#4 should be turned on, and vice versa.

The first time it triggers ZWave ID#3 off, when we turn if off ZW#5 goes off, then turn it on again, this time ZW#4 goes off (should be on tho) then we turn it off, now ZW#4 goes on (should be off), then the reverse again.

Also, I dont have any triggers for ZW5 yet in the responses.


12/7/2008 6:16:51 PM ~!~Comfort~!~Counter Changed Name:TVPower Zone:]49 No:49 Value:255
12/7/2008 6:16:51 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:16:51 PM ~!~Comfort~!~Counter Changed Name:ZWave-3 Zone:]81 No:211 Value:0
12/7/2008 6:16:51 PM ~!~Comfort~!~Counter Changed Name:CBUS-Node0-SKTA Zone:]62 No:65 Value:255
12/7/2008 6:16:51 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:16:51 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:16:52 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:16:52 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:16:52 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:16:55 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:16:56 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:17:40 PM ~!~Comfort~!~Counter Changed Name:TVPower Zone:]49 No:49 Value:0
12/7/2008 6:17:40 PM ~!~Comfort~!~Counter Changed Name:ZWave-5 Zone:]83 No:213 Value:0
12/7/2008 6:17:45 PM ~!~Comfort~!~Counter Changed Name:TVPower Zone:]49 No:49 Value:255
12/7/2008 6:17:45 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:17:45 PM ~!~Comfort~!~Counter Changed Name:ZWave-4 Zone:]82 No:212 Value:0
12/7/2008 6:17:46 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:17:46 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:17:46 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:17:49 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:17:49 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:18:08 PM ~!~Comfort~!~Counter Changed Name:TVPower Zone:]49 No:49 Value:0
12/7/2008 6:18:08 PM ~!~Comfort~!~Counter Changed Name:ZWave-4 Zone:]82 No:212 Value:255
12/7/2008 6:18:26 PM ~!~Comfort~!~Counter Changed Name:TVPower Zone:]49 No:49 Value:255
12/7/2008 6:18:27 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:18:27 PM ~!~Comfort~!~Counter Changed Name:ZWave-4 Zone:]82 No:212 Value:0
12/7/2008 6:18:27 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:18:27 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:18:27 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off
12/7/2008 6:18:30 PM ~!~Comfort~!~Output Activation: 5~IRDelay On
12/7/2008 6:18:31 PM ~!~Comfort~!~Output Activation: 5~IRDelay Off


Last edited on Sunday Dec 7th, 2008 05:31 pm by palmlodge



 Posted: Monday Dec 8th, 2008 02:02 am
   PM  Quote  Reply 
3rd Post
slychiu
Administrator


Joined: Saturday Apr 29th, 2006
Location: Singapore
Posts: 5500
Status: 
Offline

  back to top

We are on holiday in Singapore but will check it out this week



 Posted: Monday Dec 8th, 2008 06:32 am
   PM  Quote  Reply 
4th Post
palmlodge
Member
 

Joined: Thursday Dec 14th, 2006
Location: United Kingdom
Posts: 507
Status: 
Offline

  back to top

Another one.

This time, no zwave ON command sent the first time.

worked after that.

12/8/2008 6:28:46 AM      Comfort     Counter Changed Name:TVPower Zone:]49 No:49 Value:255
12/8/2008 6:28:46 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:28:47 AM      Comfort     Output Activation: 5~IRDelay Off
12/8/2008 6:28:47 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:28:47 AM      Comfort     Output Activation: 5~IRDelay Off
12/8/2008 6:28:50 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:28:51 AM      Comfort     Output Activation: 5~IRDelay Off
12/8/2008 6:29:19 AM      Comfort     Counter Changed Name:TVPower Zone:]49 No:49 Value:0
12/8/2008 6:29:20 AM      Comfort     Counter Changed Name:ZWave-4 Zone:]82 No:212 Value:0
12/8/2008 6:29:20 AM      Comfort     Counter Changed Name:TVPower Zone:]49 No:49 Value:255
12/8/2008 6:29:20 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:29:20 AM      Comfort     Counter Changed Name:ZWave-4 Zone:]82 No:212 Value:255




 Posted: Wednesday Dec 10th, 2008 02:13 am
   PM  Quote  Reply 
5th Post
leonchue
Cytech
 

Joined: Monday Aug 7th, 2006
Location: Singapore
Posts: 71
Status: 
Offline

  back to top

palmlodge wrote: Another one.

This time, no zwave ON command sent the first time.

worked after that.

12/8/2008 6:28:46 AM      Comfort     Counter Changed Name:TVPower Zone:]49 No:49 Value:255
12/8/2008 6:28:46 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:28:47 AM      Comfort     Output Activation: 5~IRDelay Off
12/8/2008 6:28:47 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:28:47 AM      Comfort     Output Activation: 5~IRDelay Off
12/8/2008 6:28:50 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:28:51 AM      Comfort     Output Activation: 5~IRDelay Off
12/8/2008 6:29:19 AM      Comfort     Counter Changed Name:TVPower Zone:]49 No:49 Value:0
12/8/2008 6:29:20 AM      Comfort     Counter Changed Name:ZWave-4 Zone:]82 No:212 Value:0
12/8/2008 6:29:20 AM      Comfort     Counter Changed Name:TVPower Zone:]49 No:49 Value:255
12/8/2008 6:29:20 AM      Comfort     Output Activation: 5~IRDelay On
12/8/2008 6:29:20 AM      Comfort     Counter Changed Name:ZWave-4 Zone:]82 No:212 Value:255



My guess is that you may be experiencing a RF problem for this one.  When the Z-Wave transmission is without an ack from the targeting module, the respective counter will not be updated.  You can verify the busy2 led (UCM/Z-Wave) is on if that is the case.  So it may be an intermittent problem. 

Check the BUSY2 LED when it happens again.



 Posted: Wednesday Dec 10th, 2008 04:55 am
   PM  Quote  Reply 
6th Post
palmlodge
Member
 

Joined: Thursday Dec 14th, 2006
Location: United Kingdom
Posts: 507
Status: 
Offline

  back to top

The ZWave UCM and this particular zwave unit are less than a metre apart , in clear line of sight.

Not only that, but sometimes the wrong counter is being changed, not just the wrong value - as in post#2 above.

Checking the Busy LED will be nigh on impossible - how long does that LED stay on after an incorrect command ?


Last edited on Wednesday Dec 10th, 2008 05:55 am by palmlodge



 Posted: Thursday Dec 18th, 2008 07:21 am
   PM  Quote  Reply 
7th Post
admin
Administrator


Joined: Saturday Mar 3rd, 2007
Location: Singapore
Posts: 1200
Status: 
Offline

  back to top

Checking the BUSY2 LED on the UCM/wave is not impossible, actually very easy. The BUSY2 LED stays on until the acknowledgment from the Zwave target device is received, or another Zwave command is sent out. Hence you can just send the command, and if it does not turn on or off the Zwave device, just stroll over to the UCM/Zwave and look at the leds. You do not need two people



 Posted: Thursday Jul 9th, 2009 07:34 am
   PM  Quote  Reply 
8th Post
TheMax74
Member


Joined: Monday Jul 16th, 2007
Location: Italy
Posts: 247
Status: 
Offline

  back to top

palmlodge, how do you have resolved these issues?



 Posted: Thursday Jul 9th, 2009 09:35 am
   PM  Quote  Reply 
9th Post
palmlodge
Member
 

Joined: Thursday Dec 14th, 2006
Location: United Kingdom
Posts: 507
Status: 
Offline

  back to top

By sticking with CBUS and X10.



 Posted: Thursday Jul 9th, 2009 09:36 am
   PM  Quote  Reply 
10th Post
TheMax74
Member


Joined: Monday Jul 16th, 2007
Location: Italy
Posts: 247
Status: 
Offline

  back to top

Hmm.. interesting. Thanks.



 Posted: Thursday Jul 9th, 2009 05:54 pm
   PM  Quote  Reply 
11th Post
admin
Administrator


Joined: Saturday Mar 3rd, 2007
Location: Singapore
Posts: 1200
Status: 
Offline

  back to top

Those were not neccesarily problems with the UCM/Zwave.
There were suggestions to follow up to check certain conditions lile the Busy 2 led which would have alllowed us to further advise
What problems are you having?