i would like to clarify an installation aspect concern Sensors (not PIR ) with PNP output NO or NC it is lightgrids and photo sensor for Extra security purposes, which it produce 12V on output when it activate. so how we connected to input channels?
thanx & B Regard
Wael
|
Posted: Tuesday Sep 16th, 2008 09:17 pm |
|
2nd Post |
WMADKOUR
Comfort Installers
Joined: | Thursday Aug 14th, 2008 |
Location: | Cairo, Egypt |
Posts: | 56 |
Status: |
Offline
|
back to top
|
i guess if not then we will use buffer relay to zone input, but if else it will be better not adding buffer instruments.
|
Posted: Wednesday Sep 17th, 2008 02:30 am |
|
3rd Post |
slychiu
Administrator
Joined: | Saturday Apr 29th, 2006 |
Location: | Singapore |
Posts: | 5499 |
Status: |
Offline
|
back to top
|
You should connect relays to the 12V outputs so that only the relay contacts are connected to the inputs. Voltages cannot be connected directly to Comfort Inputs
|
|