admin
|
When you press Away to arm to away mode, the keypad announces "Please Exit" It is waiting for you to open the entry door to exit When you open the entry door, it will stop announcing "Please`Exit" and announce "Front Door" or the name of the entry door When you close the door, after 6 seconds it will announce "Away Node" and arm to away mode If there is no zone recorded in the event log b efore Arm Failure it means that no zone, including the Entry door was open at that instant. So the arm failure was caused by the front door bot detected as having opened This may be due to an intermittent wiring problem on your front door contact or a problem with the front door contact magnetic strength. Do a Security Check F3,2 and open and close the front door many times , check if the door can be announced each time You may have to replace the contact or check the wiring Last edited on Monday May 10th, 2010 01:16 am by admin |
||||||||||||
|