I am posting this so others have a chance of not being caught out like me. My version of Ultra is quite old and therefore has the known limitation that the Counters below 128 react not only to C-Bus groups 0 through 127, but also react to 128 through 255. This effectively means that I have only half of the Group Addresses within the Lighting Application available for use. I have recently identified a need to have the status of some Comfort outputs visible to C-Bus. I chose to do this by using responses to switch on Group Addresses in a C-Bus application (57) created for the purpose. My choice of 57 follows Clipsal's recommendations. That all works fine and I can see on/off messages for the outputs. However, when I try to do things which affect both groups, I have discovered that this code (generated by Comfigurator):
or this code (manually written by me to try and fix the problem):
did not work as expected. In both cases, the second command appears on C-Bus for Application 57 (not 56 as expected). The fix is very simple - turn off the concatenation check-box against the UCM in Comfigurator. This does not seem to have had any adverse effects, but I don't have any really lengthy C-Bus commands going out from Comfort. This might be a bug, it might be expected behaviour, it might be fixed in a newer UCM version. Thinking about it, it might even be a feature in Comfigurator when it turns "code" into "actions" and finds adjacent C-Bus commands. I have found a fix that works for me. As I said, have only posted to avoid anyone else having the same challenge. Last edited on Thursday Jul 17th, 2008 11:57 am by Nick Locke |
||||||||||||
|